Waeco CR110, runs ok & cools down, switches off & on a few times before finally switching off?

Andy-in-weymouth

Free Member
Joined
Jun 2, 2019
Posts
2
Likes collected
0
Funster No
61,337
MH
Van Conversion - Sprinter
Exp
2013
Hi Guys,

First post so any help would be appreciated.

I installed this fridge (new) in a Sprinter about 4 years ago and it worked fine until the leisure batteries started to fail (it is 12v only). During that time I improved the venting which is only internal and also added 2 extra fans to circulate the air around the heat exchanger.

During the past year, the fridge works ok (replaced batteries with 2 AGM and increased wire csa to reduce voltage drops), I have noticed that the fridge cools correctly and then switches off. Within a few seconds it starts up again and runs for a few seconds before switching off. This can be repeated for another 2 or 3 times then the thermostat can be heard latching closed properly and the fridge remains off for the next 1/2 - 1 hour before the cooling cycle starts once more.

Looking at the manual, I can see it is easy to remove the thermostat and capillary tube - not sure about checking it apart from a quick visual.

Has anyone else experienced this and know of the solution - it was an expensive fridge and I don't really want to replace it if I can avoid doing so.

Many thanks,

Andy
 
:welco:
I would check it's not a problem with your batteries first. AGM batteries are pretty useless for lesiure vehicle often fail with the capacity often falling off in under 2 years.
 
We have a Waeco coolbox that can do the same thing. With ours, and it may be the same with yours, it has a low voltage cut-off. When it senses the voltage dropping it switches off and when the voltage recovers from say solar input it turns back on. This cycle repeats.

The only answer I've found is to turn it off until you have more power.
 
Thanks both, I will check that when out next - as soon as it plays up I can check the LEDS inside the fridge to see if it is low voltage.

The batteries were both new about 6 months ago and only used 3 times since. We have a 150w solar panel on the roof which keeps the batteries topped up.

I was wondering if the bi metallic strip on the thermostat had become corroded and this was causing the irregular switching off / on - a sort of arcing problem.

The fridge is cold so no problem there and it starts up correctly - just wont shut down normally until 3 or 4 attempts.

It could be voltage as you say - this was the problem when the last batteries failed - but it manifested itself on start up instead.

Thanks,

Andy
 
If you've only had cause to use your batteries 3 times in 6 months, what sort of maintenance regime have you in place for them ?
 
So it's a mechanical thermostat not electronic controller? Unusual these days.

A couple of thoughts spring to mind. You say it keeps clicking off? This could be the compressor overload Klixon, they operate when the compressor either takes too much current or simply overheats.. Check the condenser fins are clean, shine a torch in and check. It's unlikely the compressor is duff at 4 years old.

Most probably though, the thermostat may well be faulty, I've had them in the past switch randomly and temperatures fluctuating all over the place.

Tip of the day.
You can increase the thermostat differential by either lagging the phial/sensor. Or shoving it inside something dense (y)
 