Calling all the Sparks!

ShaKen

Free Member
Joined
Apr 26, 2019
Posts
478
Likes collected
841
Location
Glasgow
Funster No
60,211
MH
C Class Low Profile
Exp
A few years
I’m planning on fitting an external socket on the gable of my property to allow a short length of cable to run to my MH in my driveway for battery charging.

Now looking at a few electrical forums it appears it’s against the building / electrical regulations to run a 16A socket off of a PME TNS-C earth (a combined Earth and Neutral from the mains supply) specifically for caravans / cars.

I am going to fit a standard external, dual RCD based 13A socket and then use a 13A to 16A adaptor to feed the MH.

Can anyone advise if this is “satisfactory” as far as regs is concerned?

Any other advice / top tips re running power to MH in the driveway?
 
Last edited:

pappajohn

LIFE MEMBER
Joined
Aug 26, 2007
Posts
43,890
Likes collected
53,934
Location
Dark side of the moon
Funster No
172
Exp
Since 2005
It may contravene regs doing what you want but your still running a 13a socket off a 16a radial or 32a ring supply..... Unless you can find a source for a 13a breaker.

I'm of the opinion it's your property, if you're the only user you do as you please.... If you let your neighbour plug his lawnmower in, don't do it.

Nobody is going to come round your gaff one night and check.

I have a 16a blue socket on the (outside) back wall of my garage for plugging in my van, or I did when I had one, and that's taken from a 16a MCB. The garage consumer unit is RCD protected.
 
Last edited:

pappajohn

LIFE MEMBER
Joined
Aug 26, 2007
Posts
43,890
Likes collected
53,934
Location
Dark side of the moon
Funster No
172
Exp
Since 2005
I have a blue 2 pin & earth socket outside the garage the other end of the cable has a 13a plug, plugged into a wall socket. Wasn't worried about regs, I do all my own wiring anyway, it was just convenient.
Easiest way, just plug it in when needed.
 

old-mo

Funster
Extra Special
LIFE MEMBER
Joined
Oct 16, 2008
Posts
16,409
Likes collected
97,387
Location
Weymouth. Dorset...
Funster No
4,470
MH
Nearly aint got one.
Exp
Caravan & motorhome 45 + yrs
Easiest way, just plug it in when needed.

And you don`t have to go outside to unplug or switch off from the motor-home.. :D(y)

When it` raining... :giggler:

Subscribers  do not see these advertisements

 

StitchesnFluff

Free Member
Joined
Oct 18, 2014
Posts
1,858
Likes collected
1,157
Location
Salisbury
Funster No
33,868
MH
Hymer B598 PL
Exp
Since 2013
I have a blue 2 pin & earth socket outside the garage the other end of the cable has a 13a plug, plugged into a wall socket. Wasn't worried about regs, I do all my own wiring anyway, it was just convenient.
I have the same set up
 
Joined
Jun 29, 2015
Posts
3,744
Likes collected
62,239
Location
Southampton
Funster No
36,999
MH
caravan (for now)
Exp
on and off since 1984
I have a "home only" lead with a 13 amp plug, I plug this into an external 13 amp socket. Don't see any need for more power, I use it to charge the battery and run the fridge before a trip. Well under 13 amps.
 

Stealaway

Free Member
Joined
Jan 8, 2013
Posts
8,496
Likes collected
11,547
Location
Dronfield - Derbyshire
Funster No
24,202
MH
Burstner Lyseo 690G
Exp
Happy FLT since 2011
I’m planning on fitting an external socket on the gable of my property to allow a short length of cable to run to my MH in my driveway for battery charging.

I drilled hole through the wall directly behind a lounge socket box and simply wired it onto the ring. RCD socket and extension to van when needed.
Not very often as the solar panels tend to keep the batteries fully loaded
 

Westerham Womble

Free Member
Joined
Feb 26, 2019
Posts
49
Likes collected
33
Location
Westerham Common sometimes
Funster No
58,773
MH
Low Profile
Exp
3 years
All sounds acceptable, you’re limiting and protecting the supply at 13a and protecting all with an rcd, just make sure it’s a 30ma trip

Subscribers  do not see these advertisements

 

Camping Gaza

Free Member
Joined
May 7, 2016
Posts
993
Likes collected
1,467
Location
La Châtre, Centre-Val de Loire France
Funster No
42,958
MH
Coachbuilt Low profile
Exp
Converted a Fiat Ducato PV a while back
Of course its against regs... they don't want any old idiot installing a potential death trap outside. Heres my setup....

Works a treat.

electrical-work.jpg
 

TerryL

LIFE MEMBER
Joined
Mar 5, 2010
Posts
6,307
Likes collected
8,424
Location
North East
Funster No
10,511
MH
Low Profile
Exp
2009
Why bother? I bought a short adapter cable that takes the hookup cable at one end and a standard 3-pin plug at t'other and plug it into a standard 13 amp socket in the garage. I carry it in the van so I can do the same at my mothers house when we call in there.

Great believer in KISS principle.
 

Sundowners

LIFE MEMBER
Joined
Oct 30, 2007
Posts
3,289
Likes collected
3,571
Location
Suffolk/Central Portugal
Funster No
744
MH
A class
Exp
37 years
Of course its against regs... they don't want any old idiot installing a potential death trap outside. Heres my setup....

Works a treat.

electrical-work.jpg



I don't like that set up----- you have to take the power from van to use your keys--------- unless you have a second set of keys!!!!!!!!
 
Joined
Apr 27, 2016
Posts
7,512
Likes collected
8,988
Location
Manchester
Funster No
42,762
MH
A class Hymer
Exp
Since the 80s
it’s against the building / electrical regulations to run a 16A socket off of a PME TNS-C earth (a combined Earth and Neutral from the mains supply) specifically for caravans / cars.
To answer the OP's question, to comply completely with regs you would need to have a garage-type consumer unit, with RCD and maybe 13A or 16A MCB. More importantly it would need an earth rod into the ground, connected to the earth terminal block in the CU, which also connects to all the earth wiring. That would convert it into a TT system, which is recommended for outdoors-type circuits (provided there's an RCD)

Subscribers  do not see these advertisements

 

Westerham Womble

Free Member
Joined
Feb 26, 2019
Posts
49
Likes collected
33
Location
Westerham Common sometimes
Funster No
58,773
MH
Low Profile
Exp
3 years
You would need to complete the above if you are going to wire directly with a 16a socket, but as you’ve already said your going to plug this in to a 13a plug then whatever you plug in is just a “portable appliance” and it just needs 30ma rcd protection.
 
OP
OP
ShaKen

ShaKen

Free Member
Joined
Apr 26, 2019
Posts
478
Likes collected
841
Location
Glasgow
Funster No
60,211
MH
C Class Low Profile
Exp
A few years
To answer the OP's question, to comply completely with regs you would need to have a garage-type consumer unit, with RCD and maybe 13A or 16A MCB. More importantly it would need an earth rod into the ground, connected to the earth terminal block in the CU, which also connects to all the earth wiring. That would convert it into a TT system, which is recommended for outdoors-type circuits (provided there's an RCD)

Thanks all for the comments.

I suppose the natural next question is....

What’s to stop me putting in a 13A external RCD socket and use a cable with 13A plug on one end and a 16A female connector on the other end to plug into the MH?
 

Lenny HB

LIFE MEMBER
Joined
Oct 18, 2007
Posts
56,943
Likes collected
171,230
Location
On the coast in West Sussex
Funster No
658
MH
Carthago Compactline
Exp
Since 2008 & many years tugging
Thanks all for the comments.

I suppose the natural next question is....

What’s to stop me putting in a 13A external RCD socket and use a cable with 13A plug on one end and a 16A female connector on the other end to plug into the MH?
Nothing.
 
Joined
Aug 18, 2014
Posts
25,044
Likes collected
146,614
Location
Lorca,Murcia,Spain
Funster No
32,898
MH
Transit PVC
Exp
16 years since restarting
It may contravene regs doing what you want but your still running a 13a socket off a 16a radial or 32a ring supply..... Unless you can find a source for a 13a breaker.

Barratt's wired the garage supply of my last house like that.:mad:
 

Kannon Fodda

LIFE MEMBER
Joined
Feb 26, 2019
Posts
2,912
Likes collected
8,874
Location
Seek and Ye May Find
Funster No
58,768
MH
Autotrail V-line 540
Exp
I Make Schoolboy Errors!
You could wire a 13A spur off a ring main with a RCD unit: something like https://www.screwfix.com/p/british-general-13a-rcd-fused-spur-metal-clad/4323p. Then you can connect externally whatever cabling you like, including even the 16A type round pin so you can use your standard hook up. The concern is always overloading the wire / circuit so this way you can't get more than 13 A through your 16A rated leads, no problem. After all most sites you have your 16A rated lead yet they will only give you max 10A, often less.

Subscribers  do not see these advertisements

 
Joined
Feb 27, 2011
Posts
15,253
Likes collected
81,201
Location
UK
Funster No
15,452
MH
Self Build
Exp
Since 2005
I have a blue 2 pin & earth socket outside the garage the other end of the cable has a 13a plug, plugged into a wall socket. Wasn't worried about regs, I do all my own wiring anyway, it was just convenient.
I was a sparky as my original (ish) trade. This is exactly how I did it. However I did use an RCD similar to this in the socket I plugged it into.
https://amzn.to/2Xjs048
 
OP
OP
ShaKen

ShaKen

Free Member
Joined
Apr 26, 2019
Posts
478
Likes collected
841
Location
Glasgow
Funster No
60,211
MH
C Class Low Profile
Exp
A few years
Right, I’m going to take a spur of my ring main (back of 13A dual socket and attach to external dual 13A socket with RCD.

Then use a cable with 13A plug (fused) to 16A connector to attach to MH.

Done.
 

TerryL

LIFE MEMBER
Joined
Mar 5, 2010
Posts
6,307
Likes collected
8,424
Location
North East
Funster No
10,511
MH
Low Profile
Exp
2009
Why have a separate cable, presume you've already got a normal cable with blue plugs at both ends? Halfords do a 13 amp plug to hookup (search on W4 mains hookup adapter) for £6.

Oh I get it, your connection is going to be outside. Mine is inside the house garage (already wired through an LCD) so I don't need an external socket.
 

JFD

Joined
Apr 9, 2015
Posts
393
Likes collected
238
Location
Crawley Down, West Sussex, UK
Funster No
35,784
MH
Pilote Aventura G730
Exp
since 2014!
The only trouble with that plan is, that you are taking your ring main outside without protection. Anything you plug into the socket will be protected, but not the socket itself.

My rule is always to RCD protect inside the house to a waterproof spur outside.
 
Joined
Feb 15, 2016
Posts
659
Likes collected
1,109
Location
Essex
Funster No
41,677
MH
Coachbuilt
Exp
Since April 2016
Right, I’m going to take a spur of my ring main (back of 13A dual socket and attach to external dual 13A socket with RCD.

Then use a cable with 13A plug (fused) to 16A connector to attach to MH.

Done.
I would always recommend connecting the outside socket via a fused spur on the inside. That way you can switch the power off from the inside when not required, which would also be able to isolate it in the event of a fault on the socket.

Subscribers  do not see these advertisements

 

pappajohn

LIFE MEMBER
Joined
Aug 26, 2007
Posts
43,890
Likes collected
53,934
Location
Dark side of the moon
Funster No
172
Exp
Since 2005
The only trouble with that plan is, that you are taking your ring main outside without protection. Anything you plug into the socket will be protected, but not the socket itself.

My rule is always to RCD protect inside the house to a waterproof spur outside.
The ring main should already be protected at the consumer unit by either an RCD main switch or an RCD breaker.
Of course, there are many millions of houses which have never been updated in donkeys years.
 
OP
OP
ShaKen

ShaKen

Free Member
Joined
Apr 26, 2019
Posts
478
Likes collected
841
Location
Glasgow
Funster No
60,211
MH
C Class Low Profile
Exp
A few years
I would always recommend connecting the outside socket via a fused spur on the inside. That way you can switch the power off from the inside when not required, which would also be able to isolate it in the event of a fault on the socket.

Thanks - yes that had crossed my mind and makes obvious sense.

I’ll add that to the plan.
 
OP
OP
ShaKen

ShaKen

Free Member
Joined
Apr 26, 2019
Posts
478
Likes collected
841
Location
Glasgow
Funster No
60,211
MH
C Class Low Profile
Exp
A few years
The only trouble with that plan is, that you are taking your ring main outside without protection. Anything you plug into the socket will be protected, but not the socket itself.

My rule is always to RCD protect inside the house to a waterproof spur outside.

I’ve bought a twin RCD protected waterproof (well P66) external socket with a polycarbonate housing.

I suppose I could fit an RCD protected fused spur internally from the ring - question is can you have 2 RCD’s circuit - both at 30mA?
 
Joined
Apr 27, 2008
Posts
12,003
Likes collected
14,459
Location
Eastbourne East Sussex
Funster No
2,327
MH
Hymer low profile
Exp
Since 1972
I have a double 13a socket outside for the lawnmower No idea how it's wired but it was put in by an electrician when he rewired the house.
 
Joined
Feb 15, 2016
Posts
659
Likes collected
1,109
Location
Essex
Funster No
41,677
MH
Coachbuilt
Exp
Since April 2016
I’ve bought a twin RCD protected waterproof (well P66) external socket with a polycarbonate housing.

I suppose I could fit an RCD protected fused spur internally from the ring - question is can you have 2 RCD’s circuit - both at 30mA?
There would be no advantage in having a second RCD. As mentioned in another post if your main consumer unit has 30mA protection you wouldn't have needed an RCD socket. In the event of a fault, normally the first RCD in the system is the first one to trip, ie the one in the consumer unit will normally trip even if the one in the socket doesn't, although both may.