There is only one problem with the B10. The 2000W supply can't open it on a short fault. It will need 30A min short fault current to open it. Meaning, the 2000W supply is more likely to have a max surge of 4000W /17.4A short circuit fault amps. That puts you in the teritory of a B6 to be able to open it: 6x3=18A. For overload it may protect if it's a 2.5mm ², but for short, it won't open it, as the supply is to weak to generate/supply enough short current. Therefore a size down is preferred, to enable the magnetic trip operation. The thermal trip will work after several minutes, but the magnetic trip, it needs min 3x nominal, sometimes 5x nominal.A 10A breaker is supposed to be able to carry 10A 24/7 without tripping. It will only trip if the amps rises to above 10A, if there is a fault for example. So 7.5A for an appliance is fine.
With a 2000W inverter, chances are you would never trip a 10A breaker even if you tried, the inverter would probably cut off before the breaker tripped.