Noticed inverter cable getting warmish.

Had a look and + lead is about 2 mtrs long and - lead about 1.5 mtrs

Is this too long ?

and these were dealer fitted
20240525_160321.jpg
 
  • Like
Reactions: DBK
OP
OP
cookie
Jul 10, 2016
434
390
hucknall
Funster No
44,017
MH
Swift bolero 712sb
Exp
10 years
It's a 1000w inverter.
Maximum load 800w

Subscribers  do not see these advertisements

 
Jan 2, 2024
577
793
Lincolnshire, UK
Funster No
100,498
MH
Peugeot boxer
Exp
2020
1000w 8mm cableooks like you have 16 mm2 cable
Working on a total 6nm run you just scrape within 25 mm2,for the small additional cost and future proofing I would go 35mm2
Alternatively you need to get the inverter much nearer the battery,or at least the chassis inorder to shorten the neg cable
 

scotjimland

LIFE MEMBER
Jul 25, 2007
2,656
11,749
Funster No
15
MH
None
For an 800w load, at 12v and a 2 mt cable run

Minimum cable cross section:
25 mm²

I used this calculator

if you double the cable run, the cross section doubles to 50mm

Subscribers  do not see these advertisements

 

DBK

LIFE MEMBER
Jan 9, 2013
18,144
48,634
Plympton, Devon
Funster No
24,219
MH
PVC, Murvi Morocco
Exp
2013
Noticed inverter cable getting warmish.

Had a look and + lead is about 2 mtrs long and - lead about 1.5 mtrs

Is this too long ?

and these were dealer fitted
View attachment 901265
What do you mean by "warmish"? If it just feels slightly warm to the touch after a running the load for a while I'm not sure that is anything worry about if the load is working. The cable will be carrying something like 80 amps or perhaps a little less so it will generate a bit of heat.

You could fit a thicker cable or just get one the same size and fit in parallel to the existing one. This might be easier to do.
 
OP
OP
cookie
Jul 10, 2016
434
390
hucknall
Funster No
44,017
MH
Swift bolero 712sb
Exp
10 years
The inverter is only about 2 feet or less from the batteries so would shortening the cables cut down on heat
 

Tombola

LIFE MEMBER
Nov 21, 2020
5,031
16,218
Merseyside
Funster No
78,053
MH
Rapido 8094DF
Exp
Since 2004
If it's only 2 feet then it looks like they are long enough to cut down and add connectors to double up the cables.
2 neg and 2 pos

Subscribers  do not see these advertisements

 
Feb 15, 2016
651
1,101
Essex
Funster No
41,677
MH
Coachbuilt
Exp
Since April 2016
The inverter is only about 2 feet or less from the batteries so would shortening the cables cut down on heat
Shortening the cables won't cut down the heat on that length of cable, but it will reduce the voltage drop and losses over the total length.
 