In very hot Spain at the moment. Our Dometic air con works on the inverter but trips out as soon as we hook up to electric. Any suggestions welcome. Thanks
 
Apr 29, 2014
143
221
isle of man
Funster No
31,214
MH
coachbuilt
Exp
since 2011
I would be interested in any answers to this problem with air con as ours has also started tripping the van RCD. It also a Dometic unit.
 
Jan 19, 2014
9,395
24,781
Derbyshire
Funster No
29,757
MH
Elddis Accordo 105
Exp
since 2014
The AC needs a megger 500v insulation test, sometimes a multimeter will pick it up if bad enough. Disconnect it and measure between Live and earth then Neutral and earth, should be infinite.

Some inverters have floating earths so an RCD won't trip.

Subscribers  do not see these advertisements

 

eddie

LIFE MEMBER
Oct 4, 2007
8,157
41,270
Taunton Somerset
Funster No
540
MH
RV
Exp
since 1989
The air con works from the inverter, so unlikely that there is anything wrong with it.

The air con is "after" the inverter, the inverter is "after" the main trip and the main trip, trips when 220v is introduced so its probably a fault on the 220 VAC
 

eddie

LIFE MEMBER
Oct 4, 2007
8,157
41,270
Taunton Somerset
Funster No
540
MH
RV
Exp
since 1989
Fitted correctly the Dometic Air Con should be installed with a plug, a fused switch or a fused spur so you can isolate it from the mains for testing and or isolation in cases such as this.

So you should be able to isolate the Air Con and test again to establish if it is causing the issue
 

eddie

LIFE MEMBER
Oct 4, 2007
8,157
41,270
Taunton Somerset
Funster No
540
MH
RV
Exp
since 1989
LOL wrong thread! Sorry

Subscribers  do not see these advertisements

 
Last edited:
Aug 18, 2014
23,785
133,700
Lorca,Murcia,Spain
Funster No
32,898
MH
Transit PVC
Exp
16 years since restarting
It trips in the van and the site we're on is 10 amp electricity
It doesn't mean that the voltage will be correct. It could be dropping out on low voltage. whereas your inverter will maintain the 220v.
Common problem in spain especially if towards the end of the line on older supplies..
You need to check with a meter across the supply post of the connections at your van that you have 220v +10% or -6%.
 
Mar 6, 2008
125
137
Spixworth
Funster No
1,722
MH
Van Conversion Moto-
Exp
Since 2006
We had this problem in France recently. Symto
m:No power. Checked RCD and found tripped. Reset and tripped immediately. Reset again, this time it did not trip but site bollard did. Eventually we managed to move to another part of the site, hooked up working perfectly. Obviously a site problem. There were others problems, like the site barrier wouldn't lift, no fresh water.... A man came eventually and fixed the barrier and the water...... Sorry about going off on a tangent oops here I go again!!
 