tick59
When my motorhome is plugged into mains everything is ok ecept when you switch the water heater on then the house electrics blow. Have checked fuses in van all ok only the house electrics affected. ????
A 13a fuse will only pop on overload.Surely it is still on a plug with a 13amp fuse
I had assumed it was the house main RCD ("house electrics") rather than one particular MCB that tripped........only the house electrics affected. ????
Domestic circuits are not wired like that in the UK, or indeed in Europe. I believe some circuits in the US are, giving 120V for some appliances and 240V for higher power appliances. Some people, including me, have come across this rarely on Spanish campsites. But almost always, the neutral is at or close to ground, and the live goes +240V/-240V.I dimly remember it may be 120v shock as the 240v mains runs +120v/-120v around the neutral, or something like that.
It's certainly one of the possibilities. The MCB would trip in that case. That's why we're asking if it's an MCB or RCD that is tripping.I was just thinking that if I am on a campsite hook up and its only 4a. If i turn on the water heater by mistake it trips the Consumer unit doesn't it?
I would not be to keen on using a megger on anything electronic control or displays.The only way you can rule out the element, one way or the other, is by using an earth fault loop impedance tester, a megger
An RCD does not trip on an overload only an earth fault.I'll put money on that you have just overloaded the circuit that your EHU is on. Try an extension into the house and make sure everything in the house is off
If it still trips the switch then I'll agree its the element, if it works ok with that its just too much for the EHU circuit (whatever that is)
You are partially correct, but you can get an RCBO trips out on overload and earth fault current, basically directly swappable with mcb’sAn RCD does not trip on an overload only an earth fault.
We were talking about RCD's so I was completely rightYou are partially correct, but you can get an RCBO trips out on overload and earth fault current, basically directly swappable with mcb’s
That would only tell you if the element had continuity or not IT WOULD NOT TELL YOU IF THERE WAS AN EARTH FAULTWe had a similar discussion the other day in regard to RCD's in motorhomes. Suffice to say that if the motorhome RCD is 30 milliamp and the supply RCD is also 30 milliamp either one could trip as there is no discrimination. Many campsites have locked electrical enclosures which is a problem when the office is closed.
If the OP leaves the heater off when connecting the EHU and the supply does not fail then clearly the heater is at fault. The easiest way to test the element would be a continuity test (with power disconnected) across the terminals.
Residual current device, it trips out (disconnects) when it detect earth leakageDont know what a RCD is all i know is the house electrics switch off and the fuses trip.Works ok on gas.
RCD = Residual Current Device and it is designed to operate under an earth fault condition i.e. neutral to earth or positive to earth, but not neutral to positive (that would be a dead short and would trip the MCB).Dont know what a RCD is all i know is the house electrics switch off and the fuses trip.
To clarify; do absolutely ALL the house electrics go off, e.g. lights and power sockets? In other words there's nothing at all working in the house?Dont know what a RCD is all i know is the house electrics switch off and the fuses trip.Works ok on gas.
you may not be able to do the full test but getting a circuit from one terminal to the shell of the tank does tell you there a a break in the element ive been testing immmersions that way for yearsYou can’t check for earth leakage with a multimeter, you need an “earth fault loop impedance tester”, but as already been mention I would agree the element is probably U/S and requires replacement