Approx 36 amps but you won't see that very often.If the batteries are at 50% DOD (2 100 amp lithium) Midsummer midday what is the theoretical max amps from three 170 watt panels.
Slowly.How do you fit 6mm cable into MC4 connectors?
The victron 100/30 terminals can take 16mm cable, you need to crimp a end ferrule to go I to the connector.The maximum size cables will fit into the controller. Probably 4mm. Possibly 6mm
How many panels would that be, that’s like car battery leads ?The victron 100/30 terminals can take 16mm cable, you need to crimp a end ferrule to go I to the connector.
Edit:Approx 36 amps but you won't see that very often.
As for cable size 6mm sq from the panels to controller then 10mm sq to the battery.
Nothing to do with panels count, it’s amps and volts over distance. The 100/30 has the same connector block as the 100/50. I have 16mm2 on mine (100/50) from controller to battery. If you have a 0,1v drop from controller to battery, then your controller settings are in vain as the battery will always revive the set voltage minus the voltage drop. From controller to battery should be no voltage drop, so it can receive the full voltage. That’s why the manufacturers spec the block connector size big enough.How many panels would that be, that’s like car battery leads ?
What size cable for linking 3 x170 watt panels together then on to the Smart Solar MPPT 100/30 regulator from there to 2 x 100 lithium. Solar to regulator 3. 5 mtr. Regulator to batteries 1 mtr.