Yes, roughly. Your van is 240v and max rated at 16 amps. You will be able to run most things you run at home on a site that's got a 10 amp supply, just not all at once. If you boil a domestic kettle don't have your hairdryer going at the same time. Basically if the appliance that you want to use is providing heat it's one at a time, that heat can be a kettle, electric heater, hairdryer etc. Some of those May trip the bollard on there own but not often.Just looking on the Internet and found amps=watts/volts. I know I'm asking a silly question but are the electric hook ups 240v?
They will trip on overload as well.
If they didn't trip why so many different current rated RCDs....
32a 30ma for ring mains,
45a 30ma for electric shower and instant water heaters.
63a 30ma for consumer unit main switchs.
Again, if it doesn't trip why not make them all high amps rated then there's no risk of melting or burning out.I think it is just telling you the maximum current it can safely handle before it melts or burns out. The MCB looks after overload, the RCD detects leakage.
Apologies.... Once again mixing RCD and RCBO.For that you need an MCB. It is increasingly common to combine the MCB and RCD into a single device. When this is done, it is called an RCBO. That will trip on overload, short circuit and earth leakage.
An RCD should not be used on its own. It should have 1 or more circuit breakers fed from it which look after the individual trip currents of different circuitsAgain, if it doesn't trip why not make them all high amps rated then there's no risk of melting or burning out.
Instead of using a 32a 32ma on a ring main just fit 63a 32ma...or the same 63a 32ma on all circuits.
Sparky for near 30 years, I was absent mindedly mixing RCD for RCBOAn RCD should not be used on its own. It should have 1 or more circuit breakers fed from it which look after the individual trip currents of different circuits
As said above you can get RCBO's which are a combination of RCD and circuit breaker.
These are fine if you want RCD protection for a single circuit but an expensive option for multiple circuits, Normally have a higher current rated RCD supplying multiple circuit breaker protected circuits
It varies depending upon the cumulative power requirement in Watts which dictates the current draw in Amps of all the items you are using or that are switched 'ON' at any particular moment.Is there a way to find out what current my van draws?
230v but could be anywhere between 216.2 and 253Just looking on the Internet and found amps=watts/volts. I know I'm asking a silly question but are the electric hook ups 240v?
You can get all in once RCD and breakers all in one and that’s what most sites use.Would an RCD trip? I thought the RCD was tripped by leakage not overload. I would expect the sites 10A circuit breaker to be the first thing to operate.
That's a bit pedantic.
Rather than get into how electricery works wouldn't it be better to explain to the OP what he/she can use with a 10 amp supply, and how to do it without (hopefully) throwing the bollard out.
I thought that had already been done and poeple had moved on to the types of breakers and what effect that had on the situation.Rather than get into how electricery works wouldn't it be better to explain to the OP what he/she can use with a 10 amp supply, and how to do it without (hopefully) throwing the bollard out.
Yes it has been explained but to most people who don't understand the basics it needs explaining when they come back with more questions. I wasn't chastising anyone, I could build a control panel, and fault find it, could I rewire a house, no!I thought that had already been done and poeple had moved on to the types of breakers and what effect that had on the situation.
I now feel suitably chastised by you and won't bother with my 40 years of industial experience unless directly asked.
Pure sine wave if you want to power electronicscmcardle75
So what should I have coming out the back of my inverter please CMC ?
that i use to plung my appliances in
Agreed, but there is no 'list' of what can and can't be used.Rather than get into how electricery works wouldn't it be better to explain to the OP what he/she can use with a 10 amp supply, and how to do it without (hopefully) throwing the bollard out.