Truma combi e not heating (1 Viewer)

peter80

Free Member
May 16, 2024
5
0
Funster No
103,139
MH
Rapido 7095DF
I have a Rapido 7095DF with a Truma Combi E heater. The controls are the two knobs rather than the electronic panel. Before the winter I drained the water and boiler and left the auto frost valve open. Also left all the taps and shower open. Today I tried to put the heater on, on gas to warm the van up (without filling the water) but I get a red, constant light after a few seconds. Checked battery voltage, no problems. Tested with 230 V attached but same thing happens. Then i tried to warm up the van with electric instead, but same thing happend; red, constant light... what can be the issue?

Regards
 
May 17, 2016
3,651
7,901
Aberdeenshire
Funster No
43,137
MH
B524
Exp
2nd base
Definitely gas getting through to it? Light a hob burner for a bit just to make sure the gas is getting that far.
 
OP
OP
P

peter80

Free Member
May 16, 2024
5
0
Funster No
103,139
MH
Rapido 7095DF
Two of three hobs are working and so is the fridge, so I believe the gas is getting through...
 

Gellyneck

LIFE MEMBER
Jun 5, 2014
9,520
19,109
Scotland
Funster No
31,836
MH
C Class
Exp
More than toes wet now!
Two of three hobs are working and so is the fridge, so I believe the gas is getting through...
We sometimes have that problem when we've not used the motorhome for a while.

Whilst you're saying you're getting gas to the hob and fridge the Truma boiler can take a few attempts to fire up as it pulls the gas through. Probably something to do with a fail safe, thinks it's getting gas but it wont ignite.

Give it a few good on / off (rotate the gas / electricity / off knob to 0 / gas - wait to see it fires up / 0 / gas- wait to see it fires up / etc). When you do this you should be able to hear the igniter sparking and, if it's getting gas, the boiler firing up.

Try that and if it's still an issue get back and we'll see what next to try.

ps :HelloThere:
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
54,218
153,226
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
On those controllers the red light can also indicate low voltage, if the 12v is low the boiler won't fire up. Check the voltage at the boiler both with boiler on & off.
 
OP
OP
P

peter80

Free Member
May 16, 2024
5
0
Funster No
103,139
MH
Rapido 7095DF
Thanks for help! I´ll try your tips concerning gas, but why won´t it start on electricity?
 
OP
OP
P

peter80

Free Member
May 16, 2024
5
0
Funster No
103,139
MH
Rapido 7095DF
On those controllers the red light can also indicate low voltage, if the 12v is low the boiler won't fire up. Check the voltage at the boiler both with boiler on & off.
I´ve tried with the 230 V plugged in without result.... perhaps some issue with the battery even though the lamps are working...
 

Gellyneck

LIFE MEMBER
Jun 5, 2014
9,520
19,109
Scotland
Funster No
31,836
MH
C Class
Exp
More than toes wet now!
As Lenny says it needs a good battery supply.
Can you hear the igniter sparking?
Have you tried the heating/hot water on the 230v supply?
 
May 17, 2016
3,651
7,901
Aberdeenshire
Funster No
43,137
MH
B524
Exp
2nd base
Just checked the panel, says battery is on 13.2 V
You really need a multimeter to check the voltage at the boiler itself. A bad connection or (as I found out yesterday) a break in a old cable can cause voltage drop and cause the boiler to fail.
 

Gellyneck

LIFE MEMBER
Jun 5, 2014
9,520
19,109
Scotland
Funster No
31,836
MH
C Class
Exp
More than toes wet now!
OP is now a free member so unless subscription is paid we wont hear from him again.
 