My external wall mounted EHU socket has a normal 3 pin plug at the end inside the bungalow and is plugged in to a socket in the pantry, cannot see why you need anything special.
It is not about the power it is the type of earth, a PME earth relies on the neutral being earthed before it enters the property and is shared with nearby properties. I do remember from my training a PME earth is not suitable for a swimming pool or wet area and I have an idea it should not be used for caravan etc. but it is a long time since I did the part P course ,and after I did it all I ever did was wire up heating controls so I was hoping we had a qualified electrician on here who could advise meI’m no electrician but I would of thought providing your not drawing more than 13amps your home ring main would be ok.
This is presuming you have a more recent consumer unit with trips.
I have an outside socket that runs off our ring main ?
It is not about the power it is the type of earth, a PME earth relies on the neutral being earthed before it enters the property and is shared with nearby properties. I do remember from my training a PME earth is not suitable for a swimming pool or wet area and I have an idea it should not be used for caravan etc. but it is a long time since I did the part P course ,and after I did it all I ever did was wire up heating controls so I was hoping we had a qualified electrician on her who could advise me
Is there any metal or other earthed locally parts that could be touched if the van faulted live to chassis? Is the van on wet grass or tarmac/concrete? I would go TT but I'm not part 'P'Hi any sparks here that can offer advice on the earth for EHU. I'm putting in an outdoor socket for hook up. The bungalow has a PME earth, and I am unsure if this is suitable for hook up. It has an RCD and I could put in an earth rod and connect that socket as a TT, would that be better?
Can’t you fit a RCDI have PME and no problem with that, I don't intend to change the earth to the whole property, only the new socket for hook up, partly because the consumer unit does not have a RCD I have replaced the mcb's with rcbo's but not on the lightning so a TT system would be sub standard for this.
I work for the Electricity Board and had a fault at a farm that was PME!!I wouldn’t worry too much, I ran my farm (PME Earth) with a 6” nail as a main fuse for years, no problems sank a ” normal” earth as well, Because the supply neutral is bonded to earth in a PME system, the fault return path for both line to earth and line to neutral faults is via the combined conductor. The advantage of using the combined conductor in this way is that it provides a low impedance return path which ensures rapid disconnection of the supply under fault conditions. BUT, I’m no expert, not had a problem in 21 years though
I could, but the consumer unit is not split, so it would take everything off if it tripped, that is why I fitted rcbo's I would have to replace the consumer unit to do it right, and I am not registered or qualified to do it. A PME earth is fine in the bungalow, it is how all new properties are supplied, it is just not recommended for hook up.Can’t you fit a RCD
It is lead and I have bonded it in 10mm, so you're right, if I had remembered that I may not have ordered the earth rod. Too late now.Don't forget that in any oldish house your incoming water pipe may well be lead and this will be bonded to the earth block in the house. So whichever system of earthing you have got will also have a lovely earth rod made of many metres of lead.
Never presume anything!It is lead and I have bonded it in 10mm, so you're right, if I had remembered that I may not have ordered the earth rod. Too late now.
An unusual set of circumstances, sounds like a bodge up of the farms installation as well.I work for the Electricity Board and had a fault at a farm that was PME!!
We don’t know how it was PME because it should have be TT but the customers earth was bonded to our neutral block which WE wouldn’t have done.
This would have been like that for years and fine until a fault on the o/h network occurred!! The blue phase on the overhead line clashed with the neutral (return) wire, thus sending supply voltage down the neutral and made all the steel work on the farm LIVE!!
The farm system was quite old and had no protection which didn’t help.
This killed cattle that were leaning against the steelwork at the time it happened and continued to stay live until the linesmen arrived and pulled substation fuses.
The farmer raised the alarm when he himself had a belt from touching one of the deceased cows, it could have been a lot worse!!
This is why we don’t PME farms!!
A cheap way of gaining an earth, until the inevitable.An unusual set of circumstances, sounds like a bodge up of the farms installation as well.