Microwave on low amp supply (2 Viewers)
JohnH
404
993
Southport
Just looking
We are going to an event and the supply is only 6 amp. Is this sufficient to power a low wattage microwave? I cannot remember the formula for working out wattage to amperage etc.
I ask because that helps determine what we take in the way of food.
We have never tripped a circuit yet but have only used it on greater amp circuits.
John
Welsh girl
3,658
3,036
Globecar
I don't use mine on a low amp rating as I think it would trip it.
I then use the skillet.
Especially if you can't reset it yourself.
Techno
Jul 28, 2010
15,475
20,756
Leeds the one up North
Rapido 7090F 3 litre 160
May 2010
Yes it should cope with nothing else on at the same time like fridge and battery charger
43,348
49,550
i reckon it may trip even with all other electrical goods turned off.
A 750watt m/w oven may take 1500watts for a few seconds on startup.
1500watts = 6.25amps
Apr 22, 2013
911
661
Cotswolds
Bailey Approach 625
Since 2011
The 800W microwave fitted in our MH has an input rating of 1250W.
It runs successfully on our 1500W inverter, during operation the inverter says it is suppling 1.28kW.
6A x 230V = 1380W, you should be OK on a 6A supply, can you see the rating plate on the microwave?
Anyone know the powerfactor of a running microwave?
Gordon
43,348
49,550
Gordon
Input current and startup current are different...your calculation only allows 100watts for the startup surge current.
230v is a european 'harmonised standard' voltage....actual UK voltage is still around 240v.
19,383
30,403
We are running our 800 watt microwave on 6 amp Spanish volts no problem, as Techno says just make sure other 240 stuff is switched off.
cmcardle75
2,666
3,446
Reading
Riot Van Conversion
Remember that the typical Type B MCB is rated at continuous current. It allows plenty for startup surges already. Indeed, you need 5 times its rated value to be certain of tripping it instantaneously. You can manage double its rating for a period of many seconds.
43,348
49,550
agreed, but many hookup posts and motorhome fuseboards have type C Breakers.
Ed Excel
870
547
Ribble Valley
Coach built
Started 2007
Gordon
The input rating on your M/W includes the turntable motor, light, controls, etc, but not the starting load. Power on start up will be of the order of 1600W. Your inverter is no doubt capable of 3000W, for a short time, so it's going to be happy with your M/W start up load.
You don't say what size circuit protection supplies the M/W.
Note: p.f. of a microwave oven on defrost setting can be around 0.5
11,847
14,082
If I had a microwave (I took mine out to save space and weight) then I would run it off the inverter. If I had ehu I would use that to recharge the batteries as normal so no risk of blowing the ehu.
cmcardle75
2,666
3,446
Reading
Riot Van Conversion
A Type C breaker is even harder to trip instantaneously. It has the same thermal trip curve as a Type B, but the instantaneous action is set at a higher multiple.
Usually reserved for lifts and other devices that expect massive inrush currents. Fitted by campsites to reduce the need to constantly reset the breakers!