Would a cable run of 1.4 metres be to long to connect an inverter to my leisure battery. I am struggling to mount it any closer. BUSBY,:Sad:
 

pappajohn

LIFE MEMBER
Aug 26, 2007
43,301
49,286
Dark side of the moon
Funster No
172
Exp
Since 2005
it would be fine....if you can find one thick enough which will depend on the output watts of the inverter.

i would think starter motor or electric arc welder cable would just about do it.
 
Apr 22, 2013
911
661
Cotswolds
Funster No
25,654
MH
Bailey Approach 625
Exp
Since 2011
How big is the inverter?

This sort of thing is sold in red and black by the metre.
www.amazon.co.uk/All-Trade-Direct-Battery-Starter/dp/B00904MZVO
It would be OK for a 2000W inverter, but I suspect you will need to get the connectors crimped to the ends.

Whereas these guys will make cables to you specified length.
Link Removed
They do other sizes of cable if required.

Subscribers  do not see these advertisements

 

Ed Excel

Free Member
Nov 27, 2012
870
547
Ribble Valley
Funster No
23,815
MH
Coach built
Exp
Started 2007
You could work it out from these tables:

http://www.csecables.com/technical/table-4f1a.htm
http://www.csecables.com/technical/table-4f1b.htm

The data are for rubber insulated and sheathed cables.
First pick a cable with a suitable current rating for your load from the first table, using the following: inverter watts/12V=Amps.
Then check, on the second table for the cable chosen, the voltage drop in mV/A/m, that's the figure in the table/1000 x inverter amps x length of cable run in metres

Hope you find something for the job
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
You need to provide more information

My 1800 watt Sterling with the supplied cable thrown away as unsuitable and 35mm welding cable fitted in its place
CA_06151318351678-L.jpg
 
Apr 27, 2008
11,839
14,063
Eastbourne East Sussex
Funster No
2,327
MH
Hymer low profile
Exp
Since 1972
I would try to get closer if you can. Don't forget the cable length for the purposes of voltage drop is 2.8m not 1.4m (1.4m each way) and if you're dropping more than a volt in the cable the inverter will probably not work.
You don't give the output of the inverter and this is a critical part of the equation. Obviously if it's a titchy 300w one then its not a problem. A 3Kw one will need cables so thick they won't bend :roflmto:

Subscribers  do not see these advertisements

 
OP
OP
B
Aug 18, 2011
12,129
17,991
derbys
Funster No
17,808
MH
AUTOSLEEPER SYMBOL
Exp
since 2007.Tugger before since 1970
Inverter is 1200 watt. BUSBY:Smile:
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
running at max output that 100amps/hour out of your battery.

25mm welder cable with crimped and soldered terminals

Peak power could be double that.

My 1800watt Sterling was supplied with 4AWG (21mm) and a recommended fuse of 250amp THAT is why I replaced it with 35mm

CA_07131319314239-L.jpg
 
OP
OP
B
Aug 18, 2011
12,129
17,991
derbys
Funster No
17,808
MH
AUTOSLEEPER SYMBOL
Exp
since 2007.Tugger before since 1970
If i mount it in the glove box (how many keep gloves in it) the run from battery to inverter would be about 0.4 of a metre, would that be ok? Thanks for all previous advice from you very very Knowledgeable people. BUSBY::bigsmile:
 

lunarman

LIFE MEMBER
Sep 23, 2008
2,156
2,451
South Glos
Funster No
4,151
MH
C Class
Exp
since 1994
Is it necessary to fit some form of switch in the 12v cable? Is there any drain on the battery even with the 250v output switched off.

lunarman

Subscribers  do not see these advertisements

 

cmcardle75

LIFE MEMBER
Jun 8, 2012
2,666
3,446
Reading
Funster No
21,386
MH
Riot Van Conversion
Exp
Since 2012
If i mount it in the glove box (how many keep gloves in it) the run from battery to inverter would be about 0.4 of a metre, would that be ok? Thanks for all previous advice from you very very Knowledgeable people. BUSBY::bigsmile:

Not OK, I'm afraid. Not enough ventilation. 1.4m is fine. Just use starter motor cable. I'd probably use body earth return if you've got somewhere nearby to connect a good thick earth strap.
 