HI all, was checking my ehu lead and noticed it is only twin wired with no earth, is this ok or dangerous. I have been using it the last seven months.
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
To clarify
I fitted an RCD this protects against earth fault leakage and will trip at only 30 milli amps leakage in milliseconds .The overcurrent protection remained the job of the double pole circuit breaker supplied by the converter.
An RCBO is used for individual circuits and covers earth leakage AND overcurrent protection.

EDIT yes Rapido put the distribution boards in the garage unlike Hymers und Bursteners under seats n shit :LOL:
 
Upvote 0

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Stick one of these in, the current rating doesn't matter (but must be over 16 amps) as it is only the current carrying capacity not over current protection. The important bit is 30ma
Broken Link Removed

probably same fit for less money
Broken Link Removed

Subscribers  do not see these advertisements

 
Upvote 0
Feb 24, 2013
13,035
101,353
Bolsover, Derbyshire
Funster No
24,833
MH
Hymer S800
Exp
not long enough
Stick one of these in, the current rating doesn't matter (but must be over 16 amps) as it is only the current carrying capacity not over current protection. The important bit is 30ma
Broken Link Removed

probably same fit for less money
Broken Link Removed

I will get it done before next trip, thanks again (y)
 