Agreed, any jump leads I buy will be 35mm2 minimum. But Halfords Essentials jump leads are 8mm2 and cost £10. A good way to get thick wire, especially if you are in a hurry or have problems with online shopping.Cable tails at solar panel will probably be 4mm².
Jump leads are usually 35mm².
Jump leads won't fit the controller terminals.
Biggest you should need to avoid excessive volt drop over length will be 6mm² or 10mm².
Yes, people often go overboard with solar cabling as the biggest loss with be when the panels are producing their max output, the loss will be small in the winter when the panels are only producing a 2 or 3 amps.So can I assume 4mm cable will be fine from controller to battery if only 3-4 feet?
That chart is very poor it does not give voltage loss and is very missleading.This may helpView attachment 355480
Feel free to complain to Aqafax .That chart is very poor it does not give voltage loss and is very missleading.
e.g. for 10 amps with a cable run of 6 m it states 4.5 mm sq but states the same size cable 4.5 for 10m.
For a loss of 5% over 6m, 4 mm sq is OK but for 10m you need 6 mm sq sq cable.
Better not to post something that is misleading.Feel free to complain to Aqafax .
In theory, there will always be a voltage drop along a fuse or indeed any length of wire, however thick (assuming you are not using superconducting wires, which are not as far as I know generally available). In addition, a fuse will have a very small resistance because it is designed to heat up and melt if the current exceeds the nominal value of the fuse.do I get a voltage drop over the length of the fuse wire, approx 10mm long, or does the fuse somehow 'throttle' the leccy?
Except for cheap Chinese shite off ebay which may carry 75% MORE than its rated value before blowing getting so hot the plastic meltsFuses should not normally carry more than 75% of their rated value, and in those conditions will last indefinitely. If they are constantly run at or just below their rated value they will get hot, and loose or corroded contacts are more likely.
The Victron 75/15 has a maximum power rating of 220W so if you want to add a second panel of around 200W you need another controller. Nothing wrong in doing that and it even has advantages.Apologies for my late update, the MPPT is a Victron 75/15. The distance from panel on roof to controller is (approx) 18" ( size i'm not sure, but it does throw out 2.5 / 3A in good sunshine) , distance from controller to leisure batteries (2 x 110Ah sealed lead acid) is approx 7ft. I hope to fit another solar panel of 200 / 250w and 'assume' the Victron controller will safely handle the combined output. I'll have a look at Halfords jump leads & those male to female solar cable with MC4 plugs