Just after a bit of advice, just taken delivery of a new to me Hymer B680s and the dealer added to the existing solar panel ( 110 watt) another 120 watt , so probably 230 watt in total.
they assured me that they had fitted a new solar controller .
Having now had a really good look at it there appears to be a rather nasty little Epever EPIPDB dual solar controller and MT1 display.
We are planning to do some temporary holiday sites this year and would like as much solar as possible, would it be a good idea to fit a 300/350 watt panel and new Victron smart controller and leave the existing Epever controller in situ.
the Hymer has three Varta 95 amp AGM batteries ( unknown age but appear ok ) and a Schaudt LAS 1218 -2 charger.
Long term I would like to upgrade to Lithium
 
Apr 6, 2019
3,460
6,653
Eye, Peterborough, UK
Funster No
59,702
MH
RV
Exp
FourWinds Windsport 6.8L V10
It won't hurt to install new panel and controller. They just get on with their job depending what they sense from your battery bank.
 
Jan 8, 2013
8,400
11,386
Dronfield - Derbyshire
Funster No
24,202
MH
Burstner Lyseo 690G
Exp
Happy FLT since 2011
Having now had a really good look at it there appears to be a rather nasty little Epever EPIPDB dual solar controller and MT1 display.
That's not very nice :swear2:

That's just what I have and its worked perfectly for over 5 years.
I love the dual battery function and adjustability of the set up

IMG_20221229_155956.jpg

Subscribers  do not see these advertisements

 

Lenny HB

LIFE MEMBER
Oct 18, 2007
50,219
138,543
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
Having now had a really good look at it there appears to be a rather nasty little Epever EPIPDB dual solar controller and MT1 display.
I would ditch that controller and run everything through a Victron. A couple of years ago at a Fun rally two people were having problems with their solar in both cases it was faulty controllers of that ilk.
 
OP
OP
KUSKUS
Apr 12, 2013
1,029
2,074
Shrewsbury
Funster No
25,496
MH
Carthago 144
Exp
12
just thought about keeping it with smallest panel to charge engine battery only?

Subscribers  do not see these advertisements

 
Apr 27, 2008
11,703
13,629
Eastbourne East Sussex
Funster No
2,327
MH
Hymer low profile
Exp
Since 1972
I also have that controller. It seems to be the only one that allows proper solar charging of the vehicle battery, especially in storage when that's the one that needs priority. Many others only give a trickle to the vehicle battery. In the winter I have it set to 70% vehicle 30% leisure, the opposite when I'm using the motorhome.
Although other chargers are theoretically more efficient I keep this one for this very reason and it works fine.
 
OP
OP
KUSKUS
Apr 12, 2013
1,029
2,074
Shrewsbury
Funster No
25,496
MH
Carthago 144
Exp
12
OK sounds like a plan, did check it yesterday and it was putting 14.6 volts into the engine battery which I thought was a tad high.
 
Jun 10, 2010
8,267
19,119
Shrewsbury (sometimes)
Funster No
12,013
MH
N&B Clou Liner MAN
Exp
2006
OK sounds like a plan, did check it yesterday and it was putting 14.6 volts into the engine battery which I thought was a tad high.
if you get a votronic reg they have a separate terminal for trickle charging your starter battery. I imagine Victron will have something similar.

Subscribers  do not see these advertisements

 
OP
OP
KUSKUS
Apr 12, 2013
1,029
2,074
Shrewsbury
Funster No
25,496
MH
Carthago 144
Exp
12
Yes I had an Epever duo racer on my last Hymer that was OK.
Would like to go down the Victron route but pretty sure it won't charge engine battery.
 
Jan 8, 2013
8,400
11,386
Dronfield - Derbyshire
Funster No
24,202
MH
Burstner Lyseo 690G
Exp
Happy FLT since 2011
I’ve the sam, if you don’t mind me asking Stealaway how do you get amps through put to show?

dontnthink mine shows amps
Have a look at these instructions.
Basically move the arrow onto solar input in the centre and scroll through the options. There also current voltage and ampage readings.
You can also see the battery priority you have set up from this function.
I have 50/50 in winter and 90/10 to the hab batteries in summer when touring


s-l500.jpg
 

funflair

LIFE MEMBER
Dec 11, 2013
18,902
29,048
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
if you get a votronic reg they have a separate terminal for trickle charging your starter battery. I imagine Victron will have something similar.
No Victron don't Jon, that's why we use the battery master (y)

Subscribers  do not see these advertisements

 
OP
OP
KUSKUS
Apr 12, 2013
1,029
2,074
Shrewsbury
Funster No
25,496
MH
Carthago 144
Exp
12
The Epever solar controller in your picture is nothing like the Epipdm-com series that is installed in my Hymer but I will have a look at settings and come back to you.
 
Nov 8, 2020
597
1,183
Harpenden
Funster No
77,551
MH
Auto Trail Comanche
Exp
1998
That's not very nice :swear2:

That's just what I have and its worked perfectly for over 5 years.
I love the dual battery function and adjustability of the set up

View attachment 717621
I also have an Epever unit from Photonics Universe. It’s work faultlessly for 8 years and is fully programable for any battery system. The latest Epever app is also much better than the earlier version giving full control over the charge settings. You can even switch the load circuit on and off remotely. Super bit of kit at a very reasonable price.
7D62D7E1-0A66-4719-98E6-CC5E1092C079.jpeg
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
50,219
138,543
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
I also have an Epever unit from Photonics Universe. It’s work faultlessly for 8 years and is fully programable for any battery system. The latest Epever app is also much better than the earlier version giving full control over the charge settings. You can even switch the load circuit on and off remotely. Super bit of kit at a very reasonable price.View attachment 717995
Tat is a totally different unit, the other one is a cheap Chinese one marketed under various names.

Subscribers  do not see these advertisements

 
Jun 3, 2021
252
195
Funster No
81,675
MH
Commanche
Just after a bit of advice, just taken delivery of a new to me Hymer B680s and the dealer added to the existing solar panel ( 110 watt) another 120 watt , so probably 230 watt in total.
they assured me that they had fitted a new solar controller .
Having now had a really good look at it there appears to be a rather nasty little Epever EPIPDB dual solar controller and MT1 display.
We are planning to do some temporary holiday sites this year and would like as much solar as possible, would it be a good idea to fit a 300/350 watt panel and new Victron smart controller and leave the existing Epever controller in situ.
the Hymer has three Varta 95 amp AGM batteries ( unknown age but appear ok ) and a Schaudt LAS 1218 -2 charger.
Long term I would like to upgrade to Lithium
On the subject of adding more solar I talked to a local dealer about adding an extra panel and he said that as my panels were a few years old adding a new one could damage the old ones and recomended replacing them all at the sametime does anyone agree with that ?
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
50,219
138,543
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
On the subject of adding more solar I talked to a local dealer about adding an extra panel and he said that as my panels were a few years old adding a new one could damage the old ones and recomended replacing them all at the sametime does anyone agree with that ?
Dealer BS.
 
Nov 8, 2020
597
1,183
Harpenden
Funster No
77,551
MH
Auto Trail Comanche
Exp
1998
Tat is a totally different unit, the other one is a cheap Chinese one marketed under various names.
I see what you mean. he has one like this. They work, but cheap and cheerful. I suppose dealerships fitting solar are going to only fit the most cost efficient units.
C42B0ED2-C3BB-4729-BB9E-5DF6A00AD388.jpeg

Subscribers  do not see these advertisements

 
Jun 10, 2010
8,267
19,119
Shrewsbury (sometimes)
Funster No
12,013
MH
N&B Clou Liner MAN
Exp
2006
On the subject of adding more solar I talked to a local dealer about adding an extra panel and he said that as my panels were a few years old adding a new one could damage the old ones and recomended replacing them all at the sametime does anyone agree with that ?
incredible!! possibly a good idea to update regs, depending on whats fitted now
 

funflair

LIFE MEMBER
Dec 11, 2013
18,902
29,048
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
On the subject of adding more solar I talked to a local dealer about adding an extra panel and he said that as my panels were a few years old adding a new one could damage the old ones and recomended replacing them all at the sametime does anyone agree with that ?
No, but I would put the new one on it's own controller.
 
OP
OP
KUSKUS
Apr 12, 2013
1,029
2,074
Shrewsbury
Funster No
25,496
MH
Carthago 144
Exp
12
New solar panel on its own Victron controller and leave the other two small ones on the Chinese controller?

Subscribers  do not see these advertisements

 
May 22, 2015
1,369
2,412
Wem Shropshire
Funster No
36,507
MH
Carthago E Line 51QB
Exp
Been getting away since 2008
Maybe some more panels if you have the room and fire it all through either a Victron or Votronic controlder.
I had a Votronic on my last van and it has the extra terminal for the cab battery but at the time there wasn’t an English version for the app.
I now have a Victron in this van purely for the app and have fitted a Votronic battery master.
All works well and I’m happy with it.
 
Dec 18, 2017
62
39
Lowestoft UK
Funster No
51,677
MH
Bessacarr 524
Exp
since 2003
Just after a bit of advice, just taken delivery of a new to me Hymer B680s and the dealer added to the existing solar panel ( 110 watt) another 120 watt , so probably 230 watt in total.
they assured me that they had fitted a new solar controller .
Having now had a really good look at it there appears to be a rather nasty little Epever EPIPDB dual solar controller and MT1 display.
We are planning to do some temporary holiday sites this year and would like as much solar as possible, would it be a good idea to fit a 300/350 watt panel and new Victron smart controller and leave the existing Epever controller in situ.
the Hymer has three Varta 95 amp AGM batteries ( unknown age but appear ok ) and a Schaudt LAS 1218 -2 charger.
Long term I would like to upgrade to Lithium
Hello, I just had a read through your post, and it reads as though the "dealer" has fitted another panel to the one already on the van.
There is already a potential problem as you cannot fit different output panels together.
If there are to be more than one solar panel on your vehicle they must be of the same output ie; 2x100 or 2x150 or 4x100w etc.
If you put a 110 with a 120w you effectively now have 2 110 as the higher value will be governed by the lower if you catch my drift.
Hope that helps. Regards Trevor.
 
Jun 10, 2010
8,267
19,119
Shrewsbury (sometimes)
Funster No
12,013
MH
N&B Clou Liner MAN
Exp
2006
Hello, I just had a read through your post, and it reads as though the "dealer" has fitted another panel to the one already on the van.
There is already a potential problem as you cannot fit different output panels together.
If there are to be more than one solar panel on your vehicle they must be of the same output ie; 2x100 or 2x150 or 4x100w etc.
If you put a 110 with a 120w you effectively now have 2 110 as the higher value will be governed by the lower if you catch my drift.
Hope that helps. Regards Trevor.
are you confusing panels with batteries? I have a 100w and a 170 in one of my controllers and clamping the positive cable gives 4. 2 and 7.5 amps respectively. granted voltages need to be similar.

Subscribers  do not see these advertisements

 
Jul 5, 2013
11,512
13,336
Tunbridge Wells, Tunbridge Wells, UK
Funster No
26,797
MH
A class
Exp
Since 2013
Hello, I just had a read through your post, and it reads as though the "dealer" has fitted another panel to the one already on the van.
There is already a potential problem as you cannot fit different output panels together.
If there are to be more than one solar panel on your vehicle they must be of the same output ie; 2x100 or 2x150 or 4x100w etc.
If you put a 110 with a 120w you effectively now have 2 110 as the higher value will be governed by the lower if you catch my drift.
Hope that helps. Regards Trevor.
I think you may be confused. With panels fitted in parallel it is the voltage that should be the same, not the wattage. The voltage usually depends upon the number of cells, so just count them up.

Edit, beaten by jongood
 
Dec 18, 2017
62
39
Lowestoft UK
Funster No
51,677
MH
Bessacarr 524
Exp
since 2003
are you confusing panels with batteries? I have a 100w and a 170 in one of my controllers and clamping the positive cable gives 4. 2 and 7.5 amps respectively. granted voltages need to be similar.
No, I was referring to the original post by KUSKUS when he said, and I quote "Just after a bit of advice, just taken delivery of a new to me Hymer B680s and the dealer added to the existing solar panel ( 110 watt) another 120 watt , so probably 230 watt in total."
I had an enquiry re my adding solar panels, and talked to the specialists Sargent Electrical in Hull .
They told me you cannot mix solar panels of different watt out put. If you do then the lower panel will be the power you get from the mix.
IF, what I was told by Sargent is correct then KUSKUS now has 220 and not 230.
 

funflair

LIFE MEMBER
Dec 11, 2013
18,902
29,048
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
New solar panel on its own Victron controller and leave the other two small ones on the Chinese controller?
If the "Chinese" controller isn't MPPT I would be tempted to change that as well and get the benefit of up to 30% more power from those panels.

Subscribers  do not see these advertisements

 

Lenny HB

LIFE MEMBER
Oct 18, 2007
50,219
138,543
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
No, I was referring to the original post by KUSKUS when he said, and I quote "Just after a bit of advice, just taken delivery of a new to me Hymer B680s and the dealer added to the existing solar panel ( 110 watt) another 120 watt , so probably 230 watt in total."
I had an enquiry re my adding solar panels, and talked to the specialists Sargent Electrical in Hull .
They told me you cannot mix solar panels of different watt out put. If you do then the lower panel will be the power you get from the mix.
IF, what I was told by Sargent is correct then KUSKUS now has 220 and not 230.
That is not correct, providing the panels are the same voltage you will get 230.
 
Dec 18, 2017
62
39
Lowestoft UK
Funster No
51,677
MH
Bessacarr 524
Exp
since 2003
That is not correct, providing the panels are the same voltage you will get 230.
Ok I must be wrong if you all think so.
I am of the opinion I was simply trying to help. Perhaps this chap, who thinks he knows best can help.(personally I think he knows best)
You tell me what you think, Have a look.
Real Life Install of mismatched solar panels ->
Be interested to see what you "think"