You'll do well to get it any cheaper than that.
Do you need 2.5mm?
Most sits are limited to 6A or 10A anyway.
Peter
but get 1.5 sq and you will be in probs. on 16amp
1.5 is rated at more than 16 amp but it does not meet earth loop impedance requirements at 25 metres long. See post aboveNo you won't. 1.5mm flex is rated at 16A.
I do accept the reasons for preferring 2.5mm though
1.5 is rated at more than 16 amp but it does not meet earth loop impedance requirements at 25 metres long. See post above
Orange is recommended but the regs require BS7919 or equivalent (stamped on outer sheath)Hi all,
is there any reason not to use say 2.5mm blue arctic cable? as I can get it for £44 for a 100m roll,
I have just been given enough fittings to make up 3 leads of varying lenghts plus a RCD protected hookup point to connect just outside the garage.
Andy
Not all "arctic cable" is as flexible as you'd expect, there is a lot of cheap crap about.Nothing wrong with blue arctic cable. Its got 2.5mm conductors the same as the orange. The blue just stays flexible down to very low temperatures.
No it doesn't RCD is a residual current device with detects an imbalance of current between live and neutral. If the current out flowing around the circuit does not equal the return current it will trip, i.e. You grab a live wire and some current will flow through you to earth so the return current will be less than the outgoing current so the RCD will trip.The RCD requires an earth to operate and the earth is as far away as the cable is long.
This is why you must use the test button on your device every time you hook up somewhere new, to prove the earth.