it might be rated 16amps on the breaker or RCBO and the site owner might claim 16 amps but the connection it may only actually able to deliver 10amps.
Subscribers do not see these advertisements
France usually around 220Vish, I have known it drop to 210.
That is only as far as the camp site who would be the suppliers end user. What happens after that is down to the campsite distribution, when we were tuggers and used hook ups I've know site outlets drop to 190v. I've been on sites in France where the cables are just strung through the trees.The Electricity supplier by law must deliver 230 volts +10% - 6% (ie. between 216.2 volts and 253 volts), and to maintain the frequency at 50Hz ± 1% (ie. between 49Hz and 51Hz) over a 24 hour period.
Subscribers do not see these advertisements
All the wiring will be 3 core flex so not a lot of good.You need a clamp meter to clamp around the positive lead of your hookup cable switch everything on in the van the meter will give you the amps until it trips. Clamp meters from around £35. Lot of pi___ng around for the average person.
Belgium gets 66% of 7.2 billion for EU administration as the EU is there.....whichever way you work it that an expensive toy the UK would do well without.As usual the EU fiddled it, and NOT only on this subject.
I wonder who the biggest employer is in Sproutland
I believe the biggest receiver of EU funds is Belgium.
And I love going to Belgium. Before you jump on me.
Subscribers do not see these advertisements
You need a clamp meter to clamp around the positive lead of your hookup cable switch everything on in the van the meter will give you the amps until it trips. Clamp meters from around £35. Lot of pi___ng around for the average person.
highly unlikely .. unless it was installed by a cowboy
the upstream breaker should never be smaller than the downstream..
however.. if there are lets say 10 hook ups, all rated at 16A , the cable supply breaker may only be 45A .. so when several vans all go on full load at the same time it will trip the 45A CB .
no site supply can supply every 16A EHU socket post with 16A all at same the time..
just as a 50A supply in a house can't supply every 13A socket with 13A at the same time..
it's called diversification..
It's actually diversity that is applied not diversification if that mattersDiversification! Isn't that something that nice Mr Cameron wants us all to accept
Subscribers do not see these advertisements
It's actually diversity that is applied not diversification if that matters
Diversification! Isn't that something that nice Mr Cameron wants us all to accept
It's actually diversity that is applied not diversification if that matters