Having read the thread on EHU's I am reminded of a recent event we experienced in France, between 28/12/08 to 2/01/09, a cold spell.
We booked in, and the ehu charge was €5/day. It was confirmed the supply was 6 amps, which gives us 1380 watts. Having pitched, checked and corrected the polarity, I was asked to confirm exactly what we could run. We could run 900watts heating OR, electric ring on cooker @ 800watts OR the oil rad @ 750watts, all leaving capacity for the charger, fridge, tv, decoder, and laptop. I added that the ehu cupboard was not locked, so if we trip, we can reset it ourselves.
Next morning, returning from the shower, I was told I had made a mistake with my cals!! Why, because someone forgot to turn off the heating, when the kettle was put on the ring, drawing 1700watts. So we turned the heating up to 1800watts, with the ring still "on", now we were drawing 2600watts + fridge and charger and tv on standby!! are we on 6amps or more??
I went to the ehu point to check the mcb's, yes they were "C6" 6amp, all 7 of them, were protected by a rcd rated at 63amps!! 6 wired to cee sockets, the other one to a park light. Only two sockets were in use, ours and another camper, so I selected a mcb which was not in use and tried to trip it out. It was frozen solid and I could not trip it out. In fairness, the temperature had been zero or lower, from before our arrival to when we left.
We enjoyed a very comfortable stay, at €5 / day, very good, but seriously,
1) If the mcb is frozen, will it allow unlimited supply until it defrosts???
2) Were in the supply chain is the risk of fire, rcd, mcb, other??
Our own consumer board did not, at any time trip out, so we assume we stayed within the m/h electric constraints.
Any advice/observations aappreciated.
Nomadic
We booked in, and the ehu charge was €5/day. It was confirmed the supply was 6 amps, which gives us 1380 watts. Having pitched, checked and corrected the polarity, I was asked to confirm exactly what we could run. We could run 900watts heating OR, electric ring on cooker @ 800watts OR the oil rad @ 750watts, all leaving capacity for the charger, fridge, tv, decoder, and laptop. I added that the ehu cupboard was not locked, so if we trip, we can reset it ourselves.
Next morning, returning from the shower, I was told I had made a mistake with my cals!! Why, because someone forgot to turn off the heating, when the kettle was put on the ring, drawing 1700watts. So we turned the heating up to 1800watts, with the ring still "on", now we were drawing 2600watts + fridge and charger and tv on standby!! are we on 6amps or more??
I went to the ehu point to check the mcb's, yes they were "C6" 6amp, all 7 of them, were protected by a rcd rated at 63amps!! 6 wired to cee sockets, the other one to a park light. Only two sockets were in use, ours and another camper, so I selected a mcb which was not in use and tried to trip it out. It was frozen solid and I could not trip it out. In fairness, the temperature had been zero or lower, from before our arrival to when we left.
We enjoyed a very comfortable stay, at €5 / day, very good, but seriously,
1) If the mcb is frozen, will it allow unlimited supply until it defrosts???
2) Were in the supply chain is the risk of fire, rcd, mcb, other??
Our own consumer board did not, at any time trip out, so we assume we stayed within the m/h electric constraints.
Any advice/observations aappreciated.
Nomadic