hi , is there any reason that i shouldn't connect my tv and 12v skybox to the load terminal on my mppt solar charge controller? tv is 30 watts and box is 18 watts. at the moment i power them from the cigarette lighter socket behind the tv but the wires are very small and travel about 8 metres before they get to the sargeant power supply and then another 4 metres to the batteries which i'm sure wastes power . cheers sean
 

funflair

LIFE MEMBER
Dec 11, 2013
19,199
29,888
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
One guess would be that if you did that you would not be able to isolate it by turning the control panel off so could potentially leave a draw on your batteries. The long cable run you describe will not waste power as such but it will increase the voltage drop along the run so if the TV was shutting itself down for low volts that would be an argument for changing things.

I think the idea of the load terminal is that you can have something that is always on irrespective of the control panel setting so an entrance light or monitor of some sort.
 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,108
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
The load terminal might be set to activate on light/dark or by timer.

Subscribers  do not see these advertisements

 

Wildman

Free Member
May 30, 2008
0
8,470
Ilfracombe, Devon
Funster No
2,913
MH
Amazon Ambassador
Exp
since 1967
I run my TV and sat box via a 150W inverter connected to the load terminal. That way when the battery level falls to 50% the power is automatically cut off thereby protecting the batteries.
 

Peter A Forbes

Free Member
Nov 23, 2014
270
184
Rushden, Northants, UK
Funster No
34,314
MH
Mercedes 614D
Exp
10+
The LOAD terminals are for any load that needs to be disconnected if the battery gets down to being nearly completely exhausted.

I route all of my 12V loads through both controllers this way, thus giving the battery over-discharge protection.

Only very heavy loads such as inverters which have their own low battery cut-off need to go direct to the battery.

The output is not dependent on the solar panels operating or not, the output is maintained as long as the battery volts are above the cutoff point.

Peter
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Nice to see you have joined FUN Peter, I only just clicked who you are :xThumb:

Subscribers  do not see these advertisements

 

pappajohn

LIFE MEMBER
Aug 26, 2007
43,207
48,825
Dark side of the moon
Funster No
172
Exp
Since 2005
I have an auxilary load output on my bluesky energy controller....can be set, via internal dip switchs, to 2amps for engine battery charging or 20amps general loads.

Activates at 12.6v or above....turns off at 11.5v.
 

Peter A Forbes

Free Member
Nov 23, 2014
270
184
Rushden, Northants, UK
Funster No
34,314
MH
Mercedes 614D
Exp
10+
Thanks, Andy, I'll leave it as it is for now, It's a PITA to change a registered member's details, I know from my own forum, but thanks for the thought.

Peter
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
PITA it may be but let Jim be the judge (y)

Subscribers  do not see these advertisements

 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
BTW following a pm about suitable crimps for solar cable to terminate in this mppt unit.
CA_01021514391990-XL.jpg

I know they come with bare crimps where originally you got nothing! Peter's communication with the seller got these included but they are not very good. The main problem being length I found some long enough but I had to file them to reduce the width.
A recent search found these and they are spot on
Broken Link Removed
$(KGrHqRHJE0FHlnhl2wOBR9UNUnb8!~~60_57.JPG
 
Last edited:

Peter A Forbes

Free Member
Nov 23, 2014
270
184
Rushden, Northants, UK
Funster No
34,314
MH
Mercedes 614D
Exp
10+
I think we ended up with Yellow straight pins by memory.

Take off the Yellow crimp sleeve and solder the wire in.

The solder loop just needs easing past the plastic slot on the controller, but it does fit :)

I've got some pictures somewhere....

Broken Link Removed

Broken Link Removed

That is 6sq mm stranded cable.

Peter
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
The crimps I linked to are absolutely perfect if you just flatten the end.
Here with the rubbish supplied
CA_01051516280848-L.jpg

Right up tut chonks!
CA_01051516275770-L.jpg

Subscribers  do not see these advertisements

 

Peter A Forbes

Free Member
Nov 23, 2014
270
184
Rushden, Northants, UK
Funster No
34,314
MH
Mercedes 614D
Exp
10+
I found those a bit 'flexible', Andy, but perfectly OK for the job.

We don't use the finger terminals for anything, but do use the pins.

Bootlace ferrules are too big at 6mm, and the cable won't go in by itself, so one or the other has to be used.

The best solution as I mentioned to Eric Hsiao would be to make the terminals bigger.

Peter
 