I have a truma C6002EH boiler. I have recently noticed the water taking longer than usual to heat up.

When operating on Gas only it heats pretty quickly
When on 240v setting 2 (1800w) it heats up in about an hour
Now this is where my problem lies...
When I'm on combi / winter mode (Gas and Electric together) it's still about an hour. Surely it should be faster than either gas or electric on its own.
I think the gas isn't actually coming on to heat the water in this mode although the boiler does fire on gas for the heating side when in this mode I hear it light and kick in and out to provide extra power for the heater but makes no difference to the water.

Any ideas?

Many thanks

Wayne
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
If the power requirement is not great for space heating the boiler will give priority to the electric and save gas. If I'm correct then water heating time will not be faster unless you call for more heat in the room too.

EDIT so yes you are correct the gas is not coming on! turn up the room temperature or switch to gas mode
 
Last edited:

sdc77

Free Member
Jan 28, 2013
3,244
4,550
Weardale, Co Durham
Funster No
24,456
MH
Coachbuilt
Exp
since 2011
We have this model and have been using it in winter mode.... Water is hot in well under an hour on electric only and on both.. (I've never timed it). We recently had both elements replaced though.. So maybe that's why.

Subscribers  do not see these advertisements

 
Last edited:

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
See page 9 "mixed operation" it will confirm my previous post

Broken Link Removed
 
OP
OP
W

Wayne26

Free Member
Feb 15, 2014
4
1
Hastings
Funster No
30,120
MH
Autocruise Mustang
Exp
Since 2012
Thanks guys. After reading the manual that makes sense. I recently had both elements changed and a new PCB. I'm now thinking that only one element might be working? When I turn the electric mode on to 1 the 240 lights don't flicker slightly and I'm what hung the EHU meter to see it the light flashes any faster and it dosent seem to. When I select mode 2 both element the light do dim slightly and the meter light flashes noticibly faster.

Are the elements individually fused?
Are the any connection I can check myself or and further tests?

Thanks
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
If it doesn't function how the manual describes I would take it back to whoever you paid to fix it, I'm sure they charged plenty and it should have a warranty

Subscribers  do not see these advertisements

 

motorhomer

Free Member
May 17, 2008
680
418
South Shropshire
Funster No
2,695
MH
Van Conversion
Exp
since 2005 (but 30 years caravanning)
Took me a while to understand this, but

In SUMMER mode - ie water heating only

On elec its either 1800 or 900 watts depending on setting

On gas only its 2000 watts - ie the lowest of the 3 main automatic levels (2000, 4000, 6000)

On mixed it doesn't actually use gas it uses elec same as elec only.

In winter mode (ie heating as well as water heating)

elec only is as above

gas only is 2000, 4000, or 6000 depending on the difference between the temp setting and the actual temperature.

Mixed is 1800, 3800 or 5800 again depending on temp difference.

Running on mixed gives you no more power than gas only (in fact slightly less) but saves gas!

Hope that's clear (I Think its right!)
 