Good afternoon,
I'm hoping somebody may be able to offer a few words of direction please.
My heating has been playing up recently & has now stopped altogether.
The problem started with the system cycling on & off ie. Fan run, gas valve clicks in, system heats & blows hot air. After a while the gas valve & fan could be heard switching on & off,
initially this could be overcome by turning the stat up.
This happened again this morning but even with the stat fully up the system has stopped.
I have so far removed the combustion fan,which I thought may have siezed but it seems ok & free. If I turn the system on the fan runs & continues for a while after turning off, suggesting that it may be ok.
I would like to test the stat but have no idea as to which is which terminal where it plugs onto the circuit board.
If anyone could offer some help I would be very appreciative. It's a bit chilly at this time of year in Reading!
Thanks,
Barrie.
 
Jan 24, 2010
2,440
4,848
Funster No
10,065
MH
Adria Twin
Exp
Since 2007
have you looked at the main pcb, it has a LED that will falsh an error code?

Did have a similar thing a year or so ago, solved by cleaning the blower fan out - it was well an truly gunked up!! and it blast air through now - supposed to be cleaned 6 monthly according to truma
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
53,283
149,399
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
You could take the stat out at the other end & just short the wires out, heating should then run continually if everything else is OK.

Subscribers  do not see these advertisements

 
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
Thanks both, no led on pcb i'm afraid,have had the fan out & that's ok.
Taken stat out & measured across p o t & seems ok.
Will have to phone Truma on Monday.
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
53,283
149,399
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
Thanks both, no led on pcb i'm afraid,have had the fan out & that's ok.
Taken stat out & measured across p o t & seems ok.
Will have to phone Truma on Monday.
Not much point they don't talk to you anymore just refer you to their service agents.
 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,109
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
We often hear they are sensitive to low battery voltage.

Subscribers  do not see these advertisements

 
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
Well, despite Lennys misgivings I spoke with
Truma this morning, problem diagnosed easily to the remote temperature thermistor fitted above the door.
With this disconnected all fires up & we have masses of heat but no thermostat control.
Gets like a hot house now!
I could buy a new Truma part at an exorbitant price but could also buy just the thermistor from Maplin or RS. I wonder if anyone might know the resistance value of one please ?
Thanks for all your imputs.
Barrie.
 
  • Like
Reactions: f6c

Lenny HB

LIFE MEMBER
Oct 18, 2007
53,283
149,399
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
Only going by the response I got when I phoned them in December, you must have caught someone who got out of bed on the right side.

Subscribers  do not see these advertisements

 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Well, despite Lennys misgivings I spoke with
Truma this morning, problem diagnosed easily to the remote temperature thermistor fitted above the door.
With this disconnected all fires up & we have masses of heat but no thermostat control.
Gets like a hot house now!
I could buy a new Truma part at an exorbitant price but could also buy just the thermistor from Maplin or RS. I wonder if anyone might know the resistance value of one please ?
Thanks for all your imputs.
Barrie.
10k@25C my mate Tony tells me
 
Last edited:
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
Thanks Andy, have found the truma part is only £10, so have gone for that,hope that sorts it out.
Barrie

Subscribers  do not see these advertisements

 
Jan 28, 2008
10,111
18,361
Dovercourt, Harwich, UK
Funster No
1,353
MH
Renalt burstner
Exp
7 years campers before that
You could take the stat out at the other end & just short the wires out, heating should then run continually if everything else is OK.
be very wary of shorting out stats nowadays unless your sure its a make and break item with electronics you can do a lot of damage to very expensive pcbs
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
I'm pretty certain that shorting the thermistor STOPS the heating. removing it will allow it to run unlimited.Thus no shorting required.
 
Aug 6, 2013
11,949
16,552
Kendal, Cumbria
Funster No
27,352
MH
Le-Voyageur RX958 Pl
Exp
since 1999
Well, despite Lennys misgivings I spoke with
Truma this morning, problem diagnosed easily to the remote temperature thermistor fitted above the door.
With this disconnected all fires up & we have masses of heat but no thermostat control.
Gets like a hot house now!
I could buy a new Truma part at an exorbitant price but could also buy just the thermistor from Maplin or RS. I wonder if anyone might know the resistance value of one please ?
Thanks for all your imputs.
Barrie.
I've just repaired mine. The thermistor is a 10K type (it's marked on it) but there's another part of the spec that complicates things. 10K(ohms) is the resistance at 25 degC and the resistance falls as temp rises and rises as temp fall. The variations in response occur either side of 25degC - the variation in resistance either side of 25degC isn't the same for all 10K thermistors. I happened to have a 10K thermistor out of a dead phone battery in my junk box (I keep surprising things) and it works perfectly. You may have to try a few different ones. The one you want will almost certainly be the cheapest and most common one in the range so pick one from one of the electronics suppliers (or eBay) and try it. Just plug the bare thermistor into the two connectors hanging out of your wall & only solder it into the housing once you're happy. The value is by no means critical & I suspect the first you try will work. All you're looking for is it to switch at a comfortable temp for you when the control is somewhere between, say, 4 and 6. Alternatively the Truma part isn't too expensive - around £15 on eBay - though a lot dearer than a simple component.

Subscribers  do not see these advertisements

 
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
Oh well , back to the drawing board !
Bought & fitted a new room sensor this morning,still the same, so where now ?
Both thermistors read 10.2k.
Maybe the thermostat / switch ? I'm not sure where to probe.
I don't suppose anyone has a circuit diagram or any suggestions further please ?
In anticipation, Thanks.
Barrie.
 
Aug 6, 2013
11,949
16,552
Kendal, Cumbria
Funster No
27,352
MH
Le-Voyageur RX958 Pl
Exp
since 1999
There is no switch - just electronics that compare the control setting to the thermistor output. If disconnecting the thermistor allows the heating to run it's likely (but not certain) that the electronics are OK. That leaves the control that sets the heating level. I could not find a circuit diagram and even the circuit boards are becoming thin on the ground. Whilst I was trying to figure mine out I replaced the thermistor with a 10K pot. I used this to mimic the action of the thermistor so I could prove that the heat control was working.
 
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
Thanks Tony, I'd drawn the conclusion that maybe that was where the problem is.
When the problem started (cycling on & off ) it could be overcome by turning the stat up.
It eventually died altogether. As you say with the room sensor disconnected it runs at full tilt,
plenty of heat but no regulation.
I was hoping I might have found a diagram of the multi plug wiring to put a meter on & see
whats happening.
Don't like to replace bits willy nilly, not satisfying & too costly.
Cheers.
Barrie.

Subscribers  do not see these advertisements

 
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
Good evening.
Thought I'd just say thanks to those of you who offered me help & advice.
I managed to sort it out, the new sensor solved it.
Not sure why it didn't work first time, I did probe the switch contacts & all seemed ok.
Maybe a bit of finger trouble on my part. Still working ok now & we have heat.
Thanks again.
Barrie.
 
Feb 26, 2012
528
368
Funster No
19,975
MH
coach
Exp
Motorhome since 2006 (caravanning 38yrs)
Thank's for posting an update and glad it has been sorted
 
Dec 27, 2014
967
3,361
Funster No
34,567
be very wary of shorting out stats nowadays unless your sure its a make and break item with electronics you can do a lot of damage to very expensive pcbs
Ditto,
Lots of modern systems are not simple N/O or N/C switches.
They can send "signals" to modern systems to perform different roles........ so the above poster is absolutely correct.... proceed with caution and try to work to the schematic of the system.

Subscribers  do not see these advertisements

 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Good evening.
Thought I'd just say thanks to those of you who offered me help & advice.
I managed to sort it out, the new sensor solved it.
Not sure why it didn't work first time, I did probe the switch contacts & all seemed ok.
Maybe a bit of finger trouble on my part. Still working ok now & we have heat.
Thanks again.
Barrie.
Yes it's very strange as it should have run with the thermistor removed.
 
OP
OP
bjandlin
Feb 29, 2012
361
225
Reading & Surgeres France.
Funster No
20,006
MH
Hymer 584
Exp
Motor homing since 1998.
It did run with the thermistor disconnected Andy, on full tilt.
When I plugged the new one in it all stopped again, irrespective of the stat position.
As I say, probably finger trouble !
After this experience though I'm wondering whether to fit a switch in the line between thermistor & board connecting to give a full heat boost if we come when it's really cold.
Thanks.
Barrie.
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
It is normal practice to put the heater on FULL until it is going full blast before re adjusting to the desired setting. No need to fit a switch just put it on 9 or whatever your max point is.
Mine goes 0-60

This overcomes hysteresis in the system

Subscribers  do not see these advertisements

 
Last edited:

Join us or log in to post a reply.