One For The Techies Amongst Us B2b Competing With Solar Etc (1 Viewer)

Nigel&Debbie

Free Member
Nov 20, 2012
322
212
Full Timer
Funster No
23,740
MH
Autotrail Dakota
Exp
since Jan 2013
I have a 2013 Autotrail with the Sargent PSU. I have 200w solar system charging direct to both leisure and vehicle batteries ( by passing built in solar regulator in Sargent unit). I also have a sterling battery to battery charger.

Question. Do the different form of chargers cancel each other out / work against each other i.e. My battery to battery charger is capable of charging at up to 50 amps but only when the battery is in the right stage (discharged) however when driving down road on a sunny day, solar system is charging batteries (albeit only a few amps) enough to raise voltage to over 13 amps. Does this then trick the b2b charger to think that the batteries are charged thus causing the b2b to enter float charging mode? When you then bring in the direct charging system via the Sargent unit when engine is running, do we actually have 3 systems working against each other?

If the answer is yes, I can see an easy fix for b2b versus solar by simply fitting relay in solar system to cut connection to battery when engine is running thus allowing sterling b2b to do its job. However how do I get around the b2b versus Sargent 12v charger. I don't think it is a simple matter of installing another relay to cut connection as I have the fridge to consider!!

Anybody any thoughts or even better has anybody a solution so that I get the best out of b2b charger when driving?

Thanks

Nigel
 
Aug 6, 2013
11,951
16,556
Kendal, Cumbria
Funster No
27,352
MH
Le-Voyageur RX958 Pl
Exp
since 1999
Nothing competes. In simple terms the source supplying the highest voltage will take the bulk (or all) of the charging load. No additional control is needed or desirable.
 
OP
OP
Nigel&Debbie

Nigel&Debbie

Free Member
Nov 20, 2012
322
212
Full Timer
Funster No
23,740
MH
Autotrail Dakota
Exp
since Jan 2013
Thanks for the reply. I agree that there is no 'competition' but the issue is that the B2B (or which ever is winning) charges according to the state of the battery, which it does by sensing the voltage present in the battery. If there are two other charging sources present, then it is going to read these charging voltages as opposed to the voltage of the depleted battery.

The battery will charge eventually as when the b2b stops charging after detecting sufficient voltage the solar or Sargent chargers take over and this is repeated indefinitely. The issue is that if the other chargers were not present them the b2b would get there a lot quicker as this can charge at 50 amps.

Subscribers  do not see these advertisements

 

JJ

Mágica
May 1, 2008
19,253
47,964
Quinta Majay, Pinheiro Bordalo, Portugal
Funster No
2,459
MH
Burstner Privilege T
Exp
over 50 years
I understand that the clever way the B2B works is spoilt if there is a solar system running at the same time.

I believe the B2B intelligent system will read the voltage across the battery terminals before deciding what charge to put in.

If the panel is connected and it is sunny, the B2B charger will get a reading that makes it think the battery is full and reduce or stop it charging properly even if the battery is not full.

I was told to have a switch to disconnect the solar system when the engine is running in order to get the full benefit of the B2B charger.

JJ :cool:
 

Don Quixote

Free Member
Jul 29, 2012
2,966
5,258
Lost in La Mancha, Spain
Funster No
22,171
MH
VW T6 Campervan
Exp
Not long enough, but a little common sense helps..........
Well I have the B2B fitted and no matter what charge the solar is or has put in the batteries after being parked up for 5/7 days when I start the engine after a few seconds the B2B will start feeding amps ( from 45amps depending on how long I have been parked ) then after 15/20 minutes static running or driving to next place will drop to 4/5 amps and then around 30 minute mark goes to .5amp. This is with solar connect as well. I must admit I have never been told or even thought of removing the solar feed whilst using B2B as always thought it make no difference.
 
Nov 13, 2012
440
438
Somerset
Funster No
23,678
MH
coachbuilt
Exp
since 2000
I always switch off my solar panel when driving as it is not needed. I can select which ever battery needs charging. I had the sergeant charger fail and it was very useful to have the solar direct to batteries. Sargent are crafty they rivet the cover on the panel to stop easy access to do repairs

Subscribers  do not see these advertisements

 

funman

Free Member
Aug 6, 2010
98
23
Somerset
Funster No
13,054
MH
la Strada Hi Top
Exp
Since 1972
I found that the Sterling overrides the solar panel, so if the battery is fairly well charged before starting a long drive on a sunny day, then I switch off the input to the Sterling (using a home-installed switch). My reasons for this are:

1. Solar power is free; power from the alternator is costing me extra diesel.
2. The Sterling makes a noise.
3. The Sterling interferes with the radio
4. The more I use the Sterling, the more likely it is to break down and have to be replaced for the 4th time.

By the way, I know it says on the box that the Sterling is rated at 50 Amps, but even Sterling themselves admitted to me once that the 50 Amps is what they draw from the alternator / starter battery. What they give out to your leisure battery is considerably less - on mine, with a very flat leisure battery, about 35 amps is the most I've ever measured.
 

JJ

Mágica
May 1, 2008
19,253
47,964
Quinta Majay, Pinheiro Bordalo, Portugal
Funster No
2,459
MH
Burstner Privilege T
Exp
over 50 years
Well, I am only repeating what I have been told and I am no expert...

I am not really interested in the constant Amps, Volts, Watts discussions that are never far away when (male) motorhomers get together but...

If your B2B is putting in "from 45 amps" for 15/20 mins (let's say 40 amps for 20 mins) I reckon that to be around 14.85 amp hours your B2B has put in before it drops down to the second phase of charging.

I presume there to be all sorts of other factors involved (battery condition, temperature etc) but that doesn't seem like much of a first phase charge to me...

but then what do I know?

I still suspect that the B2B receives misleading information if, when it monitors the battery voltage at start up, the solar panel(s) are is pumping up that voltage at the terminals.

But then what I really, really think is this...

When you switch on a light, does it light up?

When you open a tap to fill the kettle, does water come out?

When you plug in your smartphone into the USB charger thingy in your cig lighter socket, does it go "beep" and start charging?

If answer to the three questions above is "yes" then all is fine with your van electrics!

Now... which route down to Faro did you take?

JJ :cool:
 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,109
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
Question. Do the different form of chargers cancel each other out / work against each other

Nigel

What a delicious question. You'd get a PhD for giving a definitive answer.

All will be measuring the single battery voltage.
All will take different actions depending on that voltage.
The voltage that trips different actions will be different for every one even if, say, all recognise a trip point of 13.6V. The tolerance will be different between them.

Fire it all up:
Unit A -- I'm dead simple I want 13.6V
Unit B -- I charge to 14.2V then drop back to 13.6V
Unit C -- I charge to 15V for 5 mins then 14.2V then 13.6V

C wins for 5 mins cutting out A+B.
B wins next because it outputs 14.25 with the clock ticking.
B drops to 13.6 so is cut off by C which is still on it's 14.2 stage.
C drops to 13.6 but is really 13.55 and B wins with 13.6.
A says F*** This I can't compete.

You are well set up for "gitter" the voltage gittering 0.5V or so as they interact under differing conditions.

So god knows what could happen under the million combinations of charging conditions. Nothing bad but not as good as you would like maybe.

Subscribers  do not see these advertisements

 
Apr 9, 2014
1,307
6,595
Lincs
Funster No
30,922
MH
Coachbuilt
Exp
2012
I have a 2013 Autotrail with the Sargent PSU. I have 200w solar system charging direct to both leisure and vehicle batteries ( by passing built in solar regulator in Sargent unit). I also have a sterling battery to battery charger.

Just curious and there maybe an obvious answer to this but why by pass the solar regulator in the Sargent unit?
 

Don Quixote

Free Member
Jul 29, 2012
2,966
5,258
Lost in La Mancha, Spain
Funster No
22,171
MH
VW T6 Campervan
Exp
Not long enough, but a little common sense helps..........
Well, I'm changing nothing in my MH as all appears to be working as is.................

Subscribers  do not see these advertisements

 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
My B2B only charges my leisure batteries.
My 300 watt of solar charges my 500ah inverter batteries and sends surplus to the leisures via a CBE CSB2
My leisure batteries top up the engine battery via a "battery master"
I can at the flick of a switch combine or change which bank feeds the habitation or charge everything from multiple sources
The inverter is also a 3 stage mains charger so the inverter batteries don't draw from the CBE charger as it would struggle with 6 batteries.
Usually everything stays topped up :LOL:
 

gibbon

Free Member
Feb 25, 2013
307
325
Shatterford
Funster No
24,838
MH
C class
Exp
Since 2005
The idea of conflicting tech never occurred to me.
I have an Amperor 3 stage power supply when plugged in to mains.
130w solar going through a ctek 250s dual as an mppt controller which is also a dc to dc charger when driving.
This seems to be keeping the hab & starter battery in a happy place.
I think I'll be leaving well alone(y)
 
OP
OP
Nigel&Debbie

Nigel&Debbie

Free Member
Nov 20, 2012
322
212
Full Timer
Funster No
23,740
MH
Autotrail Dakota
Exp
since Jan 2013
Thanks for all the replies.

After speaking with Sargent, sterling and a specialist auto electrician, here is their advice and solution.

Firstly, as pointed out by @hilldweller there is definitely a conflict between the 3 chargers which will cause glitching as they compete /swap amongst each other as the voltage in the battery changes.

All three specialists agreed that it is best to have only one charging system working at any one time.

I have a Sargent ec500 control unit fitted to my autotrail which works by having a direct link from the vehicle alternator to the hab batteries when the engine is running. The vehicle alternator is effectively the charger when engine is running.

To resolve the problem, I have done the following:

1. On the feed from the hab battery to the ec500 unit, I have fitted a relay which is operated by an ignition operated live feed from the vehicle (taken from feed to the 12aux power supply).

2. On the 12v positive from the victron mpp250 solar controller, fitted in series a relay (as above) and a second relay(closed type) operated by the live 12v feed from the mains operated battery charger.

The result

When driving, both the feeds from the solar regulator and ec500 unit 'charger' are cancelled, leaving the sterling b2b to fully manage the hab battery charging. The fridge 12v is totally unaffected by above and works properly.

As soon as ignition is switched off, the first relay changes and the solar regulator takes over as the only charging unit.

If I have 240v hook up, and I turn on the separate charger this causes second relay to operate on solar 12v feed to batteries, effectively turning solar off and allowing mains charger to control 12v system.

Thanks for all the help on the forum and also to the 3 specialists

Subscribers  do not see these advertisements

 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,109
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
If I have 240v hook up, and I turn on the separate charger this causes second relay to operate on solar 12v feed to batteries, effectively turning solar off and allowing mains charger to control 12v system.

I think that's a No No.

Normally you must connect the solar controller to battery THEN the solar panel. Stage one allows the solar controller to sense the battery voltage.

So to kill solar fit the relay in the panel feed.
 
OP
OP
Nigel&Debbie

Nigel&Debbie

Free Member
Nov 20, 2012
322
212
Full Timer
Funster No
23,740
MH
Autotrail Dakota
Exp
since Jan 2013
I think that's a No No.

Normally you must connect the solar controller to battery THEN the solar panel. Stage one allows the solar controller to sense the battery voltage.

So to kill solar fit the relay in the panel feed.[/QUOTE

That's what has been done I.e relays are on the feed from panels to regulator. Sorry for typo
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
My mppt regulator does not conflict with my inverter charger it simply goes straight into float mode if the charger is switched on. If I put a large load like the kettle on the mppt will throw as many amps in as it can to support the mains charger until the load is removed and the voltage recovers

Subscribers  do not see these advertisements

 

Don Quixote

Free Member
Jul 29, 2012
2,966
5,258
Lost in La Mancha, Spain
Funster No
22,171
MH
VW T6 Campervan
Exp
Not long enough, but a little common sense helps..........
As I have the same MPPT as Andy and as I have stated "won't be changing a thing" to date works for me as is....... B2B / MPPT / on board EHU charger.......... all working...... sorted.
 

eddie

LIFE MEMBER
Oct 4, 2007
8,144
41,181
Taunton Somerset
Funster No
540
MH
RV
Exp
since 1989
I wonder how many days a year that it is sunny enough for the solar to make any difference what so ever?

Many answers to questions are a "theoretical precise" answer over what actually happens. I personally am against adding relays (consume power) and switches people forget) and get into a pickle.

Like mixing lead acid batteries in parallel with GEL batteries. Post on here that you've done this and you would be hounded out like a baying crowd chasing a witch lol.

Hymer do!

Eddie
 
Apr 18, 2009
3,569
3,367
Englishman in Mid Wales
Funster No
6,340
MH
Hymer B584, A Class
Exp
Not long enough!
I wonder how many days a year that it is sunny enough for the solar to make any difference what so ever?

Many answers to questions are a "theoretical precise" answer over what actually happens. I personally am against adding relays (consume power) and switches people forget) and get into a pickle.

Like mixing lead acid batteries in parallel with GEL batteries. Post on here that you've done this and you would be hounded out like a baying crowd chasing a witch lol.

Hymer do!

Eddie


And I love Hymer:notworthy2::cooler:

Subscribers  do not see these advertisements

 

Lenny HB

LIFE MEMBER
Oct 18, 2007
53,315
149,507
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
I wonder how many days a year that it is sunny enough for the solar to make any difference what so ever?

Many answers to questions are a "theoretical precise" answer over what actually happens. I personally am against adding relays (consume power) and switches people forget) and get into a pickle.

Like mixing lead acid batteries in parallel with GEL batteries. Post on here that you've done this and you would be hounded out like a baying crowd chasing a witch lol.

Hymer do!

Eddie
You baiting us Eddie?:)
I am sure you know Hymer no longer fit Gel batteries, also when they did the Elektroblock only supplies a trickle charge of up to 2 amps to the engine battery and only once the leisure battery is 80% charged, far better than ending up with a flat engine battery. Also Hymer have never paralleled Gel & Wet leisure batteries which you imply (by not giving the full story).
 

eddie

LIFE MEMBER
Oct 4, 2007
8,144
41,181
Taunton Somerset
Funster No
540
MH
RV
Exp
since 1989
You baiting us Eddie?:)
I am sure you know Hymer no longer fit Gel batteries, also when they did the Elektroblock only supplies a trickle charge of up to 2 amps to the engine battery and only once the leisure battery is 80% charged, far better than ending up with a flat engine battery. Also Hymer have never paralleled Gel & Wet leisure batteries which you imply (by not giving the full story).
LOL What happened when you started the engine?
 

eddie

LIFE MEMBER
Oct 4, 2007
8,144
41,181
Taunton Somerset
Funster No
540
MH
RV
Exp
since 1989
I think that you'll find that the batteries are simply in parallel and they rely on the voltage drop of the reduced wire gauge to sort things out.

The reality of what I am saying is that "Lots" of things are done that one paper should be avoided, but in practice if all works.

A bit like phoning Van Bitz and asking "Should I disconnect my battery before connecting a battery charger"?

Would get you a different answer than "Do you disconnect your battery before connecting a battery charger"?

Subscribers  do not see these advertisements

 

Lenny HB

LIFE MEMBER
Oct 18, 2007
53,315
149,507
On the coast in West Sussex
Funster No
658
MH
Hymer B678 DL
Exp
Since 2008 & many years tugging
I'm fairly certain that the Eletroblock charges via it's own circuitry that performs similar to a B2B unit & batteries are not just paralleled.
 
Feb 27, 2011
14,710
75,766
UK
Funster No
15,452
MH
Self Build
Exp
Since 2005
There are some solar regulators that require the batteries to be connected before the solar panels. Mike was telling me at stratford that a certain regulator goes into 24V mode by default. Someone had one fitted and when the owner went to get some welding done the batteries were disconnected. Upon reconnection the regulator went into 24v mode and cooked the 12v batteries.

Sounds like a really crappy regulator design to me but may be worth noting.

I would personally have the relay on the solar panel side as my regulators instruction manual states to connect batteries first before connecting solar panel.

On mine I have 2 battery isolator type switches with the removable handles. One of the handles has been remove from the cab, the other moves between the B2B and solar switches so I can only have one connected at a time. (or will be when I get round to finishing off the refit I started last month :whistle: )
 
Feb 8, 2014
1,662
4,650
Sheffield
Funster No
30,022
MH
Eldis Majestic 115
Exp
Vans and tugs since mid 70's
What a delicious question. You'd get a PhD for giving a definitive answer.

All will be measuring the single battery voltage.
All will take different actions depending on that voltage.
The voltage that trips different actions will be different for every one even if, say, all recognise a trip point of 13.6V. The tolerance will be different between them.

Fire it all up:
Unit A -- I'm dead simple I want 13.6V
Unit B -- I charge to 14.2V then drop back to 13.6V
Unit C -- I charge to 15V for 5 mins then 14.2V then 13.6V

C wins for 5 mins cutting out A+B.
B wins next because it outputs 14.25 with the clock ticking.
B drops to 13.6 so is cut off by C which is still on it's 14.2 stage.
C drops to 13.6 but is really 13.55 and B wins with 13.6.
A says F*** This I can't compete.

You are well set up for "gitter" the voltage gittering 0.5V or so as they interact under differing conditions.

So god knows what could happen under the million combinations of charging conditions. Nothing bad but not as good as you would like maybe.

Definite PhD earned by @hilldweller here (y)(y)(y) love his answer and it makes good sense. My only worry would be all 3 units competing and maybe over-working unnecessarily?