We are going to an event and the supply is only 6 amp. Is this sufficient to power a low wattage microwave? I cannot remember the formula for working out wattage to amperage etc.
I ask because that helps determine what we take in the way of food.
We have never tripped a circuit yet but have only used it on greater amp circuits.
John
 

Welsh girl

LIFE MEMBER
Nov 7, 2009
3,658
3,036
Funster No
9,222
MH
Globecar
Exp
Since 2004
I don't use mine on a low amp rating as I think it would trip it.
I then use the skillet.
Especially if you can't reset it yourself.
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,756
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Yes it should cope with nothing else on at the same time like fridge and battery charger

Subscribers  do not see these advertisements

 
Last edited:

pappajohn

LIFE MEMBER
Aug 26, 2007
43,289
49,223
Dark side of the moon
Funster No
172
Exp
Since 2005
i reckon it may trip even with all other electrical goods turned off.

A 750watt m/w oven may take 1500watts for a few seconds on startup.

1500watts = 6.25amps
 
Apr 22, 2013
911
661
Cotswolds
Funster No
25,654
MH
Bailey Approach 625
Exp
Since 2011
The 800W microwave fitted in our MH has an input rating of 1250W.
It runs successfully on our 1500W inverter, during operation the inverter says it is suppling 1.28kW.

6A x 230V = 1380W, you should be OK on a 6A supply, can you see the rating plate on the microwave?

Anyone know the powerfactor of a running microwave?

Gordon

Subscribers  do not see these advertisements

 

pappajohn

LIFE MEMBER
Aug 26, 2007
43,289
49,223
Dark side of the moon
Funster No
172
Exp
Since 2005
The 800W microwave fitted in our MH has an input rating of 1250W.
It runs successfully on our 1500W inverter, during operation the inverter says it is suppling 1.28kW.

6A x 230V = 1380W, you should be OK on a 6A supply, can you see the rating plate on the microwave?

Anyone know the powerfactor of a running microwave?

Gordon

Input current and startup current are different...your calculation only allows 100watts for the startup surge current.

230v is a european 'harmonised standard' voltage....actual UK voltage is still around 240v.
 
Last edited:

funflair

LIFE MEMBER
Dec 11, 2013
19,286
30,053
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
We are running our 800 watt microwave on 6 amp Spanish volts no problem, as Techno says just make sure other 240 stuff is switched off.

Martin

Subscribers  do not see these advertisements

 

cmcardle75

LIFE MEMBER
Jun 8, 2012
2,666
3,446
Reading
Funster No
21,386
MH
Riot Van Conversion
Exp
Since 2012
Input current and startup current are different...your calculation only allows 100watts for the startup surge current.

230v is a european 'harmonised standard' voltage....actual UK voltage is still around 240v.

Remember that the typical Type B MCB is rated at continuous current. It allows plenty for startup surges already. Indeed, you need 5 times its rated value to be certain of tripping it instantaneously. You can manage double its rating for a period of many seconds.
 

pappajohn

LIFE MEMBER
Aug 26, 2007
43,289
49,223
Dark side of the moon
Funster No
172
Exp
Since 2005
Remember that the typical Type B MCB is rated at continuous current. It allows plenty for startup surges already. Indeed, you need 5 times its rated value to be certain of tripping it instantaneously. You can manage double its rating for a period of many seconds.

agreed, but many hookup posts and motorhome fuseboards have type C Breakers.
 

Ed Excel

Free Member
Nov 27, 2012
870
547
Ribble Valley
Funster No
23,815
MH
Coach built
Exp
Started 2007
The 800W microwave fitted in our MH has an input rating of 1250W.
It runs successfully on our 1500W inverter, during operation the inverter says it is suppling 1.28kW.

6A x 230V = 1380W, you should be OK on a 6A supply, can you see the rating plate on the microwave?

Anyone know the powerfactor of a running microwave?

Gordon

The input rating on your M/W includes the turntable motor, light, controls, etc, but not the starting load. Power on start up will be of the order of 1600W. Your inverter is no doubt capable of 3000W, for a short time, so it's going to be happy with your M/W start up load.

You don't say what size circuit protection supplies the M/W.

Note: p.f. of a microwave oven on defrost setting can be around 0.5

Subscribers  do not see these advertisements

 
Apr 27, 2008
11,837
14,056
Eastbourne East Sussex
Funster No
2,327
MH
Hymer low profile
Exp
Since 1972
If I had a microwave (I took mine out to save space and weight) then I would run it off the inverter. If I had ehu I would use that to recharge the batteries as normal so no risk of blowing the ehu.
 

cmcardle75

LIFE MEMBER
Jun 8, 2012
2,666
3,446
Reading
Funster No
21,386
MH
Riot Van Conversion
Exp
Since 2012
agreed, but many hookup posts and motorhome fuseboards have type C Breakers.

A Type C breaker is even harder to trip instantaneously. It has the same thermal trip curve as a Type B, but the instantaneous action is set at a higher multiple.

Usually reserved for lifts and other devices that expect massive inrush currents. Fitted by campsites to reduce the need to constantly reset the breakers!
 