Mains Electric Wiring (1 Viewer)

IrasciBill

Free Member
Mar 6, 2010
194
37
SW Scotland
Funster No
10,521
MH
Auto-Roller 500
Exp
Since 2009 (after many years camping)
Been doing some re-wiring of the mains electric wiring on my son's camper van. Think the existing installation was done by Heath Robinson when on turbo-enthusiasm! :whatthe: The entire system needs tidying up and a large measure of thought given to the safety side of things. (It had a battery charger in the gas cupboard!) :whatthe::whatthe:
The existing set-up has an earth bond from the mains earth terminal to the van body. Is this normal? Is it a good idea? I would value your thoughts. :Smile:
 

scotjimland

LIFE MEMBER
Jul 25, 2007
2,084
9,014
Suffolk Coastal District, UK
Funster No
15
MH
Timberland
The existing set-up has an earth bond from the mains earth terminal to the van body. Is this normal? Is it a good idea? I would value your thoughts. :Smile:

Hi Bill

More than a good idea, the earth bonding from the mains earth terminal to the van chassis/body is essential ..

9. - All metal parts of the caravan, with the exception of metal sheets forming part of the structure, must be bonded together and to a circuit protective conductor, which must not be smaller than 4 mm² except where it forms part of a sheathed cable or is enclosed in conduit.
Here are the regulations for a caravan. same as a motorhome , should keep you right

http://www.tlc-direct.co.uk/Book/7.9.2.htm
 
Last edited:
OP
OP
IrasciBill

IrasciBill

Free Member
Mar 6, 2010
194
37
SW Scotland
Funster No
10,521
MH
Auto-Roller 500
Exp
Since 2009 (after many years camping)
Thanks

Many thanks Jim. The link is really useful.
When it comes to electrics, I'm a competent amateur (my background is mainly in mechanical engineering, hydraulics and pneumatics)- sadly the person who did the conversion must have been at the loo when the competent bit was being given out.
Most of what I've been doing this weekend was getting the main circuit breakers and several other components away from the gas cupboard and fitting an external hook-up connection.
So far all I have done is in accordance with the regs you linked to. :thumb::thumb:

Subscribers  do not see these advertisements

 

Wintonian

Free Member
Nov 30, 2009
122
1
Brittany, France
Funster No
9,522
MH
A Class
Exp
2
While making a few changes to my UK bought Hymer in order to get it registered here in France, I decided to change all the 13 amp UK sockets for European sockets. The previous owner was clearly not even a competent amateur. He had installed a nice shiny brass double socket next to the kitchen area and connected it using table lamp flex, taking that through the wardrobe to the consumer unit. The thought of connecting a 2Kw fire, and, perhaps an electric kettle to that is not good!:Eeek:

I replaced the cable with 2.5sq mm French cable and did the same with the other sockets.

The French regs are very tight for old Camping Cars and the gas and electrical installations were checked thoroughly by Bureau Veritas (at a cost to me of 250 Euros!).:Angry: That is mandatory for older imports. At least the gas installation was thoroughly checked in my presence.
 

Wildman

Free Member
May 30, 2008
0
8,470
Ilfracombe, Devon
Funster No
2,913
MH
Amazon Ambassador
Exp
since 1967
The existing set-up has an earth bond from the mains earth terminal to the van body. Is this normal? Is it a good idea? I would value your thoughts. :Smile:
My thoughts are simple but not what you would like to hear. You are obviously not qualified to undertake the work you are proposing which raises 2 questions,

1) the legality of you actually doing the work and
2) the advisability of you doing it. A little knowledge is a dangerous thing. It is not your life you could be putting at risk.

Most of us have undertaken these jobs in the past but the elf and safety issues have tightened up. If you need to be qualified to wire a house then the same applies to a motorhome.

sorry if it is not the sort of comment you were looking for.
 

teensvan

Free Member
Jul 25, 2009
63
1
Fulltime in Motorhome
Funster No
7,653
MH
Coachbuilt
Exp
5
Hi.

Sorry to put a downer on it if you have to ask any questions on the subject of rewiring you should not be doing this type of job. Leave it to an expert.

steve & ann ---------- teensvan

Subscribers  do not see these advertisements

 

Wintonian

Free Member
Nov 30, 2009
122
1
Brittany, France
Funster No
9,522
MH
A Class
Exp
2
My thoughts are simple but not what you would like to hear. You are obviously not qualified to undertake the work you are proposing which raises 2 questions,

1) the legality of you actually doing the work and
2) the advisability of you doing it. A little knowledge is a dangerous thing. It is not your life you could be putting at risk.

Most of us have undertaken these jobs in the past but the elf and safety issues have tightened up. If you need to be qualified to wire a house then the same applies to a motorhome.

This is the sort of comment that generally comes from an electrician, most of whom are well qualified in their trade, but, unfortunately, not in the law.

I am not a qualified electrician and yet, three years ago, did a complete re-wire of my son's house in England. Every piece of wiring was taken out and I re-did the whole 3 bedroomed, two storey house.

Prior to starting the work I notified the Local Authority Building Control department and paid them a fee (only £129, which covered all the subsequent inspections). All councils are obliged, by law, to do this. My plans and circuits were first inspected by their appointed inspector who then told me to proceed. He was kind enough to offer some valuable advice.

After I completed all the work two inspectors came to do a thorough test of the installation, which it passed with zero faults.

All this was legal, despite me not being a qualified electrician. The law actually only requires work to be carried out by "a competent person".

Provided you do your homework (I bought a copy of the IEEE Regs) and are proficient with the use of tools there is no reason why any competent and intelligent person should not be able to do any of the jobs required on a Motor Home.
 

Wildman

Free Member
May 30, 2008
0
8,470
Ilfracombe, Devon
Funster No
2,913
MH
Amazon Ambassador
Exp
since 1967
This is the sort of comment that generally comes from an electrician, most of whom are well qualified in their trade, but, unfortunately, not in the law.

I am not a qualified electrician and yet, three years ago, did a complete re-wire of my son's house in England. Every piece of wiring was taken out and I re-did the whole 3 bedroomed, two storey house.

Prior to starting the work I notified the Local Authority Building Control department and paid them a fee (only £129, which covered all the subsequent inspections). All councils are obliged, by law, to do this. My plans and circuits were first inspected by their appointed inspector who then told me to proceed. He was kind enough to offer some valuable advice.

After I completed all the work two inspectors came to do a thorough test of the installation, which it passed with zero faults.

All this was legal, despite me not being a qualified electrician. The law actually only requires work to be carried out by "a competent person".

Provided you do your homework (I bought a copy of the IEEE Regs) and are proficient with the use of tools there is no reason why any competent and intelligent person should not be able to do any of the jobs required on a Motor Home.
a useful post and the reason for my query is defined in the last paragraph.

The law actually only requires work to be carried out by "a competent person".

a competent person would not need to ask about earth bonding so I still stick to my original statement.
Plus you had the work checked by a qualified tester. Full marks to you. I have been pilloried in the past for mentioning various qualifications so will not do so again.
However I do know what I am talking about.
 

bevo

Free Member
Nov 15, 2008
218
4
north west
Funster No
4,941
MH
c class
Exp
3
mains electrics

hi bill
i too rewired my house, easy peasy (as long as your not colour blind)
have added extra sockets in the van (7) no problem.
if you feel your confident enough go for it.
but the main earth for the van has to be through the outside socket to the sites electric box.
i would have trouble finding an earth through my tyres.
my take on the qualified people doing it is that if someone does is for you they need to be qualified.
but if you do it yourself it don't count.
just use flexible 2.5 sq cable in the van.
good luck

Subscribers  do not see these advertisements

 

shortcircuit

Free Member
Sep 13, 2007
162
0
Funster No
284
This is the sort of comment that generally comes from an electrician, most of whom are well qualified in their trade, but, unfortunately, not in the law.

I am not a qualified electrician and yet, three years ago, did a complete re-wire of my son's house in England. Every piece of wiring was taken out and I re-did the whole 3 bedroomed, two storey house.

Prior to starting the work I notified the Local Authority Building Control department and paid them a fee (only £129, which covered all the subsequent inspections). All councils are obliged, by law, to do this. My plans and circuits were first inspected by their appointed inspector who then told me to proceed. He was kind enough to offer some valuable advice.

After I completed all the work two inspectors came to do a thorough test of the installation, which it passed with zero faults.

All this was legal, despite me not being a qualified electrician. The law actually only requires work to be carried out by "a competent person".

Provided you do your homework (I bought a copy of the IEEE Regs) and are proficient with the use of tools there is no reason why any competent and intelligent person should not be able to do any of the jobs required on a Motor Home.

This type of posting has been done to death on various forums. However I would suspect the inspectors report would have been filled with the usual disclaimers as "After I completed all the work" they would have no idea as to how you had carried out the work and would provide a report to keep themselves clean. Insurance companies love the DIYs as they can walk away.
 
Jul 29, 2007
6,526
39,280
Ipswich
Funster No
32
MH
RV and PVC
Exp
30 years
It always gets my interest when people say that only qualified people should touch electrics. Having rewired and wired new builds, fitted kitchens, bedrooms, bathrooms, boilers and worked on vehicles its always been my opinion that household electricians are at the bottom of the pile.

Plumbers and mechanics need to know far more about a greater variety of appliances/vehicles than electricians, and can by making simple mistakes cause greater danger to the public, while electricians almost have to make deliberate mistakes to cause any harm at all.

If you shouldn't touch electrics then that goes double for you car.

Olley
 

Geo

Trader - Funster
Jul 29, 2007
11,757
14,563
Mansfield,Notts
Funster No
35
MH
Autotrail Tracker FB
Exp
45 +years with breaks
You may be interested to know that I have just had my Rv electrical safety inspection and certification carried out as reqd every 3 years :RollEyes:
yes a proper inspection and test, a hidden fault was found in the slide area cabling no trips being set off but a higher than acceptable resistance (fire risk?) without the fully qualifyed electrician it would have been the fire brigade who told me about it:RollEyes:
How do you test for that type of problem Olley?the equipment used was extreamly complicated and exspensive, capable of testing even the breakers for the time they took to work, do your breakers work fast enough?or do they just work, or dont they work at all???
How many diy ers inform their insurance of the modifications carried out
Inspections and certification for Caravans European and American RVswill be on offer here very soon
Geo

Subscribers  do not see these advertisements

 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,108
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
How do you test for that type of problem Olley?
Geo

Dead easy - measure voltage. Plug in kettle, measure voltage.

There are two ways - get a moron to use an expensive device that shows the obvious or get someone with a brain to use basic tools and fully analyse the results.

You know PAT tests. Plug into meter press button issue sticker. BUT does the moron spot the loose screws, the kinky flex about to fail, the wrong fuse, the sign of a bit of heating, the smell ?

It's the same with you Geo. The Moron in the main dealership - computer says replace, X, Y, Z. Geo says "useless twat all you do is clean that and adjust it, been doing it for 100 years".
 

shortcircuit

Free Member
Sep 13, 2007
162
0
Funster No
284
Dead easy - measure voltage. Plug in kettle, measure voltage.

There are two ways - get a moron to use an expensive device that shows the obvious or get someone with a brain to use basic tools and fully analyse the results.

You know PAT tests. Plug into meter press button issue sticker. BUT does the moron spot the loose screws, the kinky flex about to fail, the wrong fuse, the sign of a bit of heating, the smell ?

It's the same with you Geo. The Moron in the main dealership - computer says replace, X, Y, Z. Geo says "useless twat all you do is clean that and adjust it, been doing it for 100 years".


Sorry Brian but it is just not as simple as that. Your basic multimeter is unable to carry out the test properly. Not going into a technical debate but it is horses for courses and the tester should be competent along with the proper equipment
 
Jul 29, 2007
6,526
39,280
Ipswich
Funster No
32
MH
RV and PVC
Exp
30 years
Hi Geo quite likely a dirty connection, unlikely to cause a fire unless your fuses are incorrectly rated for the cable size. Much more likely that you would have trouble deploying your slides.

Your right, your MCB's might not operate, and they aren't simple to test, but they are very reliable, I don't know the MTBF but it must be very high. Wire fuses are KISS proof by nature. You don't test the speed of MCB's operating, you test the amount of current going through them before they operate, and compare that with what type they are. A type "B" trips at between 3-5 times its rated current.

Your overall electrical safety should be by RCCD and this can be tested by simply pressing the button.

You obviously take your electrical safety very seriously, and are to be congratulated for that,:Cool: however I would guess most owners of caravans/motorhomes/RV don't have any testing done, as most home owners don't either, and fires from correctly wired and fused circuits are I would think very rare, its the incorrectly wired and fused circuits that cause problems.

Olley

Subscribers  do not see these advertisements

 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,108
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
Sorry Brian but it is just not as simple as that. Your basic multimeter is unable to carry out the test properly. Not going into a technical debate

Explain please. You have already started a technical debate.

Geo: "higher than acceptable resistance (fire risk?)" "How do you test for that type of problem Olley?"

Brian: Load circuit and calculate resistance.

Where have I gone wrong ?
 

shortcircuit

Free Member
Sep 13, 2007
162
0
Funster No
284
Explain please. You have already started a technical debate.

Geo: "higher than acceptable resistance (fire risk?)" "How do you test for that type of problem Olley?"

Brian: Load circuit and calculate resistance.

Where have I gone wrong ?

The test instrument required to carry out the test in accordance with the regulations needs to pass a current of 20mA through the circuit for continuity and 500volts for insulation tests .
 

hilldweller

LIFE MEMBER
Dec 5, 2008
605
36,108
Macclesfield
Funster No
5,089
MH
Zilch Mk1
Exp
From Aug 2007
The test instrument required to carry out the test in accordance with the regulations needs to pass a current of 20mA through the circuit for continuity and 500volts for insulation tests .

We are talking at cross purposes here. Geo asked a theoretical "how would you....high resistance" and I answered "load and calculate", leakage did not come into it. You are talking regs, which is fair enough in the context of a vehicle inspection but this is not what Geo asked.

Subscribers  do not see these advertisements

 

Geo

Trader - Funster
Jul 29, 2007
11,757
14,563
Mansfield,Notts
Funster No
35
MH
Autotrail Tracker FB
Exp
45 +years with breaks
And where is your certificate of compliance at the end of all this testing:Doh:
You will more than likely be asked for it before any claim is paid out and that applies to bricks and morter homes as well
Caravans and Motor homes 3 yearly, Domestic Dwellings 5 yearly,
Garages and Comercial premisses 5 yearly

This believe it or not has come about at the shock horror reaction of my insurance company at my answer to their question "have any changes been made to the vehicle"
I said yes Ive just changed the TV:Eeek::Eeek::Eeek::Eeek: and then followed the Inquisition.
after that, I clamped up
I did not volenteer any info about a 240v conversion untill I had a cert to prove safe installation
I'm just closing as many Insurance get outs as possible:thumb:
 

scotjimland

LIFE MEMBER
Jul 25, 2007
2,084
9,014
Suffolk Coastal District, UK
Funster No
15
MH
Timberland
To get back to the OP , Bill is doing a rewire on a camper, he has identified several problems and has asked advice.

The fact that he identified problems and sought advice shows a clear commitment to safety.

He adds in his second post " When it comes to electrics, I'm a competent amateur (my background is mainly in mechanical engineering, hydraulics and pneumatics)"

So he is competent to use hand tools, can follow schematics, understand maths, read and understand regulations and follow instructions.. Given his experience, rewiring a camper should be well within his capabilities.

I gave advice and pointed to a site for further help and guidance.. he didn't come on here looking for a lambasting about his competency.. there is another site that dishes that out in shed loads. :RollEyes:

The only decent piece of additional advice to come out of the thread is to have his installation inspected and certificated on completion which I fully endorse.

Been doing some re-wiring of the mains electric wiring on my son's camper van. Think the existing installation was done by Heath Robinson when on turbo-enthusiasm! :whatthe: The entire system needs tidying up and a large measure of thought given to the safety side of things. (It had a battery charger in the gas cupboard!) :whatthe::whatthe:
The existing set-up has an earth bond from the mains earth terminal to the van body. Is this normal? Is it a good idea? I would value your thoughts. :Smile:
 

pappajohn

LIFE MEMBER
Aug 26, 2007
43,207
48,802
Dark side of the moon
Funster No
172
Exp
Since 2005
anyone can rewire their own property whether they know what they're doing or not BUT, only a qualified electrician can carry out a final inspection and test and issue a certificate.

part P of the wiring regs forbids ANYONE NOT QUALIFIED AND REGISTERED from working on kitchen and bathroom circuits...even the house owner.
the electrician needn't be registered but the company he works for must be.

it may be possible to work out resistances and loads etc using a basic multimeter but that aint enough.

all completion certificates must be sign by a registered NIC-CEI electrician and also includes the electricians enrolment No and the serial No of the test equipment used.
he then becomes responsible for that installation.

legally, the final connection to the meter can only be carries out by the electricity company...no-one else, and they wont do it without a certificate.(unless an isolator switch has been PREVIOUSLY fitted and connected, BY THEM, between meter and consumer unit)

Subscribers  do not see these advertisements

 
Aug 9, 2008
203
7
Lanner - Cornwall
Funster No
3,621
MH
A Class RV
Exp
20 + Years
legally, the final connection to the meter can only be carries out by the electricity company...no-one else, and they wont do it without a certificate.(unless an isolator switch has been PREVIOUSLY fitted and connected, BY THEM, between meter and consumer unit)



Read with interest the previous Posts. So you are saying that if you have an Isolator switch installed by the Electricity Company between Consumer Unit and the Meter you dont need a certificate??????? which is good as I have one and I have always done my own electrics, as I worked in the Electrical/Communications Industry ALL my working life but prior to all this new legalisation came into force

Brian
 

pappajohn

LIFE MEMBER
Aug 26, 2007
43,207
48,802
Dark side of the moon
Funster No
172
Exp
Since 2005
Read with interest the previous Posts. So you are saying that if you have an Isolator switch installed by the Electricity Company between Consumer Unit and the Meter you dont need a certificate??????? which is good as I have one and I have always done my own electrics, as I worked in the Electrical/Communications Industry ALL my working life but prior to all this new legalisation came into force

Brian

yes, you still need the certificate but your sparky can connect to the leccy boards supply instead of having to get them to do it at their convenience.
 
OP
OP
IrasciBill

IrasciBill

Free Member
Mar 6, 2010
194
37
SW Scotland
Funster No
10,521
MH
Auto-Roller 500
Exp
Since 2009 (after many years camping)
Response

Hi Guys
Many thanks for ALL of the contributions to my question - even the ones which went off at a tangent! :Smile: If I may be permitted a few comments though :-
Only ScotJimland actually answered the original question and I am indebted to Jim for pointing me in the right direction. I'll assume that the rest of you were equally happy with Jim's reply and chose not to duplicate!
I was not asking about earth bonding in general but about whether the 230V system should be earthed to the body which also carries the 12V system return. It struck me that, in event of a fault, there was a possibility of damage to the van's electronics but no-one else seems to have shared my concerns. (I understand that European built MHs don't always have such an earth connection!)

My thoughts are simple but not what you would like to hear. You are obviously not qualified to undertake the work you are proposing which raises 2 questions,

1) the legality of you actually doing the work and
2) the advisability of you doing it. A little knowledge is a dangerous thing. It is not your life you could be putting at risk.

Most of us have undertaken these jobs in the past but the elf and safety issues have tightened up. If you need to be qualified to wire a house then the same applies to a motorhome.

sorry if it is not the sort of comment you were looking for.

Wildman, whilst I agree with the sentiment of your contribution, please don't confuse "qualified" with "competent" - they are not the same!
I am not committing an offence by re-wiring my son's camper and would certainly NOT put his life, or that of anyone else at risk. In fact, it was the existing dangerous wiring installation that prompted my action. Pity the person who carried out the installation didn't have the benefit of your knowledge! However, as Wintonian pointed out the requirement is that such work be carried out by "a competent person"

Hi.

Sorry to put a downer on it if you have to ask any questions on the subject of rewiring you should not be doing this type of job. Leave it to an expert.

steve & ann ---------- teensvan

Teensvan, the only person who doesn't need to ask questions is a know-all - not an expert.

However, as I said at the begining of this ramble, I thank all of you for your contributions and, just for the record, I am actually qualified to test the installation (and have the certificate to prove it :thumb:) and have access to the proper equipment for doing so!

Subscribers  do not see these advertisements

 

shortcircuit

Free Member
Sep 13, 2007
162
0
Funster No
284
Bill
I trust you noted that Jims link leads to a site that refers to the 16th Edition of the Regs when we have been using the 17th Edition for some time now. Have not looked to see what differences are in but you may wish to check yourself.
 