Invertor load draw question

Discussion in 'Tech/Mech General' started by Peter & Elaine, Aug 2, 2016.

  1. Peter & Elaine

    Peter & Elaine Funster

    Joined:
    Aug 30, 2012
    Messages:
    3,967
    Likes Received:
    6,462
    Location:
    Roobarb land
    is I correct in assuming that a
    12 volt to 240 volt invertor with a 800 watt constant load a a surge load of 1400 watt
    Has the potential to pull a currant from batterys of 115 amp at full load and around 60 amp at 800 watt
    The resson I ask is the supply cables provided look much too small 50 amp maybe
    They are about a quarter inch diameter
    My old 2200 watt one where about half inch diameter that I am using now but would like to get rid of so I can tidy up a bit and lighter cables would make it easer to do so
    The cable run lenth battery to invertor would be about 3 foot

    All help greatfully received
    Peter
     
  2. Steve

    Steve Funster Life Member

    Joined:
    May 8, 2013
    Messages:
    1,550
    Likes Received:
    1,792
    Location:
    Compton Berkshire
    in my opinion a 115amp load at 3ft you should be using 25mm cable. 16mm will work but likely to get warm so using power. dont forget fuse.
     
    Last edited: Aug 2, 2016
    • Like Like x 1
  3. xsparks

    xsparks Funster

    Joined:
    Mar 11, 2013
    Messages:
    133
    Likes Received:
    66
    Location:
    Gillingham
    That's the cross sectional area not the diameter.
     
  4. scotjimland

    scotjimland Funster Life Member

    Joined:
    Jul 25, 2007
    Messages:
    28,934
    Likes Received:
    25,574
    Location:
    .
  5. Mr Mousy

    Mr Mousy Funster Life Member

    Joined:
    Sep 9, 2013
    Messages:
    246
    Likes Received:
    605
    Location:
    SA14 9NH
    Peter, I have some cable that may do the job - which you are welcome to. Are you going to Malvern? If not I will post.
    Regards Martin

    @Peter & Elaine
     
    Last edited: Aug 2, 2016
    • Like Like x 1
  6. John Laidler

    John Laidler Funster

    Joined:
    Jan 9, 2013
    Messages:
    8,573
    Likes Received:
    11,553
    Location:
    Plympton, Devon
  7. Peter & Elaine

    Peter & Elaine Funster

    Joined:
    Aug 30, 2012
    Messages:
    3,967
    Likes Received:
    6,462
    Location:
    Roobarb land
    Thanks for your kind offer but I can get my hands any size cable at the place I work part time
     
  8. Peter & Elaine

    Peter & Elaine Funster

    Joined:
    Aug 30, 2012
    Messages:
    3,967
    Likes Received:
    6,462
    Location:
    Roobarb land
    After looking though advice here and in links provided I think I have Sused out my problem
    I have been confusing cross section and diameter
    I have some good quality heat resistant 8 mil diameter cable that very flexible that I think will do what I want
    And when considering that the max load we would would ever put on the inverter is 700 watt about 60 amp battery load I am fairly sure it will be more than good enough with a 80 amp fuse on battery end
    Unless someone tells me my calcs are wrong
    Cheers
     