    Location:
    Hornchurch
    About to install a 1500W inverter. All going well until I have been forced to secure it about 1.25 m from batteries. The leads that came with the inverter are now to short. Some advice from you experts would be most grateful . Am I correct in working out that I now need to run the cable in a thicker grade as the distance from the batteries has now increased. If that is the case would 8mm thick be ample
     
  2. jonandshell

    jonandshell Funster

    Joined:
    Dec 12, 2010
    Messages:
    5,261
    Likes Received:
    7,881
    Location:
    West Norfolk
    No it wouldn't!

    Your inverter is rated at 1500 watts, that would normally be a constant rating. You should assume double that for peak current.
    An inverter is also rarely more than 90% efficient, that means you should add 10%. Therefore you should calculate peak current for 3300 watts.

    At 11 volts, the voltage your batteries will be at under heavy load, the DC current could be as high as 300 amps!
    This is a worse case, but 35mm cable would be a safe bet, given the length required.
    I reckon you would be OK with 25mm though.
     
    • Like Like x 1
  3. Zains Pops

    Zains Pops Funster

    Joined:
    Sep 10, 2013
    Messages:
    718
    Likes Received:
    3,874
    Location:
    Chelmsford Essex
  4. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    I expect the OP means 8mm diameter which is not a recognised way of sizing cable in relation to current carrying capacity. John is referring to 25mm cross sectional area of the copper conductor.(y)
     
  5. PJGWiltshire

    PJGWiltshire Funster

    Joined:
    Mar 11, 2013
    Messages:
    263
    Likes Received:
    165
    Location:
    Hornchurch
    Thanks for your help, have also tracked down an old post where Andy states 35mm, so I will go with that. I have worked out the fuse as 125A (1500/12v) would this be be suitable or should I get a 300A mentioned by John
     
  6. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
  7. SUGGY

    SUGGY Funster Life Member

    Joined:
    Nov 23, 2011
    Messages:
    893
    Likes Received:
    1,629
    Location:
    scunthorpe
    My inverter is 3kw peak 2.5kw constant running ,
    i conected it up using 100 amp unipren cable .
    When using the Remoska it takes around 50 amp from the batteries ,
     
  8. PJGWiltshire

    PJGWiltshire Funster

    Joined:
    Mar 11, 2013
    Messages:
    263
    Likes Received:
    165
    Location:
    Hornchurch
    Many thanks Andy and everyone else. Shall get on and order.
     
  9. rapido convert

    rapido convert

    Joined:
    Feb 26, 2015
    Messages:
    58
    Likes Received:
    113
    Location:
    knutsford cheshire
    Hi, i use heavy duty jump leads to connect my batteries and inverter, it is much cheaper to buy a set off fleabay then cut the clamps off, the last set i purchased were 30mm copper and 2.8 meters long they cost £14·00 delivered, ps my inverter is 2000w /4000w peak power pure sinwave and is 1.5 meters away from the lead battery in my battery bank.
    This set up has served me well without over heating /power loss for many years i have a 1kw solar system and only camp without hook up.
    Cheers
    Andy.
     
    • Like Like x 4
  10. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    I use the Blue sea brand fuse holder, very substantial quality kit.
    [​IMG]
     
  11. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    [​IMG]
     
  12. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    [​IMG]
     
  13. PJGWiltshire

    PJGWiltshire Funster

    Joined:
    Mar 11, 2013
    Messages:
    263
    Likes Received:
    165
    Location:
    Hornchurch
    what is the switch over junction for
     
  14. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    300amp isolator
     
  15. PJGWiltshire

    PJGWiltshire Funster

    Joined:
    Mar 11, 2013
    Messages:
    263
    Likes Received:
    165
    Location:
    Hornchurch
    Everything ordered, should be here midweek. Looks simple enough to clip together and the photograph guide is a dream. Is that four(4) batteries I can see and are they the cables for the solar panel
     
  16. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    yes
     
  17. PJGWiltshire

    PJGWiltshire Funster

    Joined:
    Mar 11, 2013
    Messages:
    263
    Likes Received:
    165
    Location:
    Hornchurch
    looks very tidy
     
  18. Steve

    Steve Funster Life Member

    Joined:
    May 8, 2013
    Messages:
    1,551
    Likes Received:
    1,796
    Location:
    Compton Berkshire
    25mm ok but 35mm better.
     
  19. PJGWiltshire

    PJGWiltshire Funster

    Joined:
    Mar 11, 2013
    Messages:
    263
    Likes Received:
    165
    Location:
    Hornchurch
    Looks like I have made an error when buying the inverter. Checking it again I now note that it is a duel supply type. Not sure why this is so. Is it a case of running a positive and negative to both terminals from the battery or can I go through a junction box for both + and -, with one single feed to the battery via a 200A on the + (Intend using 25mm2 (230A) cable and Isolator.
     
  20. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,860
    Likes Received:
    14,520
    Location:
    Leeds the one up North
    Picture?
     
Loading...

Share This Page