    After a long thought I decided to position a power point outside for the MH. After getting all the cable, sockets etc. I then found out it needed a "qualified electrician" to either fit or sign off so I contacted said electrician who has just finished upgrading the old fuse box for a nice new consumer unit, checked if we needed a complete re-wire (fortunately not required as old (over 38 years old) wiring still has good insulation) and wired in the external socket. Today, plugged in the van to top up batteries and the whole lot has tripped in the house. Have been checking the van for faults and after consulting the handbook for my Autocruise Wentworth I find I have modified wiring. At some stage in its life it has had wiring for an inverter to be fitted and it seems somewhere between the mains input socket and the van consumer unit is a heavy duty relay (found behind the heater, accessed after removing 2 drawers.) I have had SWMBO indoors resetting the house trip (not circuit but main trip) every time I switch on the van circuit for heater, boiler, charger and fridge but the relay seems to be the culprit. I have an inverter which clips on the battery terminals and a fly lead plugs into the inverter giving power to lights, charger and sockets. I can only think this relay is there to avoid running the boiler and heater on inverted mains. Never had a problem with old fuse box at home nor when plugging in on site. Any ideas anyone please.
     
  2. Badknee

    Badknee Funster

    Joined:
    Aug 25, 2014
    Messages:
    3,640
    Likes Received:
    15,218
    Location:
    notloB
    Hmmmm, everything in van ok. Have new socket fitted not ok. I suspect new socket.
    Can you plug the van into another socket say through a door/window to test?
     
    • Thanks Thanks x 1
  3. ceejayt

    ceejayt Funster Life Member

    Joined:
    Aug 12, 2015
    Messages:
    381
    Likes Received:
    489
    Location:
    York
    If you normally plug your van in when out and about then it can't be anything to do with the van. It has to be either the new socket or possibly you have damaged your hook up cable?
     
    • Thanks Thanks x 1
  4. xsparks

    xsparks Funster

    Joined:
    Mar 11, 2013
    Messages:
    132
    Likes Received:
    66
    Location:
    Gillingham
    I would guess that the relay switches skts between mains input and inverter. I'm guessing that the new fuse board you had fitted now has an earth leakage trip and that is what's tripping. I would suspect a neutral earth fault which would not have been apparent beforehand.
     
    • Like Like x 1
    • Useful Useful x 1
    • Informative Informative x 1
  5. Lenny HB

    Lenny HB Funster

    Joined:
    Oct 18, 2007
    Messages:
    5,215
    Likes Received:
    5,010
    Location:
    West Sussex
    They changed that a few years ago only applies to kitchens and bathrooms now. I still do everything myself gas & electric I don't want any of those bodging so called professions on my property.:)
    I assume it is the RCD tripping in the house, unkely to be the relay, you need to disconnect everything in the van then with it connected to the mains reconnect one item at a time until you find what is tripping it. At a guess more likely to be a heating element Truma or fridge.
     
    • Thanks Thanks x 1
  6. Badknee

    Badknee Funster

    Joined:
    Aug 25, 2014
    Messages:
    3,640
    Likes Received:
    15,218
    Location:
    notloB
    But why now all of a sudden, all that's changed it seems is a new outdoor socket has been installed on the side of the house, why condemn the MoHo?
     
    • Thanks Thanks x 1
  7. John Laidler

    John Laidler Funster

    Joined:
    Jan 9, 2013
    Messages:
    8,564
    Likes Received:
    11,539
    Location:
    Plympton, Devon
    If you have had a new consumer unit fitted it will be much more sensitive than the old one. We had a hidden electrical problem in the house which only came to light when we had new circuit breakers installed in the house consumer unit. Although the old ones were only ten years old they were unable to detect a short between earth and neutral which tripped the new ones.

    The fact that you have not had problems on sites doesn't mean anything as their circuit breakers are probably not as sensitiv as the ones now fitted in your house.

    I suggest get your electrician back and ask him to do a megger test on the MH, I strongly suspect this will identify a wiring fault.
     
    • Thanks Thanks x 1
  8. Lenny HB

    Lenny HB Funster

    Joined:
    Oct 18, 2007
    Messages:
    5,215
    Likes Received:
    5,010
    Location:
    West Sussex
    Just had a new consumer unit fitted probably connecting before without an RCD in the house, but you would expect the RCD in the van to have tripped. Problem with 2 RCD in series the one with the shortest trip time will trip first. Agree may not be the van, but if it only happens with the van plugged in it points to the van.
    Worth checking the hook up lead to make sure there is no moisture inside the plug & socket. Only other way I can think is if the earth in the socket at one or other end has been crossed with live or neutral then it would trip when you plugged the van in.
     
    • Thanks Thanks x 1
  9. bertiebasset

    bertiebasset Funster

    Joined:
    Jun 16, 2014
    Messages:
    291
    Likes Received:
    288
    Location:
    NOTTINGHAM
    Thanks for the replies.
    Thanks ceejayt, Hookup cable new and ok. Socket new as is fused spur. I have now connected van and switched off the 3 breakers in there, house system ok.

    Thanks xsparks, Have to agree with you.

    Thanks Lenny. I have the van in pieces now. The consumer unit in the van has 3 circuits. I am able to switch 2 on but on switching the 3rd it trips the mains in the house. All circuits are in the off position- Heater, Boiler, Fridge and charger, The first 3 have isolator sockets fitted and are in the off position. I have pulled the connector from the charger. 230v Lights (touch on/off) now removed. So all circuits off. If I try the test button it cuts off the power at the van board but when switching back on there is a click from behind heater (this relay) and the house RCD cuts out.

    Thanks Paul, Will try with usual hookup lead tomorrow when I have rebuilt van.
    20160125_160909.jpg
    van RCD with cover removed. LH input, Middle heater, fridge, boiler and 12v Charger, RH sockets

    20160125_161000.jpg

    Relay behind drawers ??
     
  10. PeteH

    PeteH Funster

    Joined:
    Nov 22, 2007
    Messages:
    1,751
    Likes Received:
    2,158
    Location:
    East Yorkshire
    Can I clarify? 1) You had the house Consumer unit upgraded. 2) Did you connect the MoHo after the upgrade was done AND BEFORE the new Socket was fitted?. OR 3) only after the New Socket was put into service?. IF (2) and no trip, then the new socket is suspect. IF (3) then the new Consumer unit is Likely to be far more "Sensitive" and has detected a problem IN THE VAN.

    EDIT:- Update;_ Which I note you have discovered since I posted!!!.

    Pete
     
    • Thanks Thanks x 1
  11. xsparks

    xsparks Funster

    Joined:
    Mar 11, 2013
    Messages:
    132
    Likes Received:
    66
    Location:
    Gillingham
    Now that you have located the circuit you will now need to gradually separate its components until you are able to reset the rcd .
     
    • Useful Useful x 1
  12. bertiebasset

    bertiebasset Funster

    Joined:
    Jun 16, 2014
    Messages:
    291
    Likes Received:
    288
    Location:
    NOTTINGHAM
    Thanks Pete. We have had a new consumer unit in to replace an old fuse box. I had run the cable from the new outside socket indoors (I actually connected the armoured cable to a 3pin plug and connected the van OK....to fuse box) When the electrical work was carried out the outside socket was connected via a fused spur and on its own RCD. That was last Thursday. The fun began today. Really think it is sensitively of new RCD unit. Only option is to remove relay and see.
     
    • Thanks Thanks x 1
  13. bertiebasset

    bertiebasset Funster

    Joined:
    Jun 16, 2014
    Messages:
    291
    Likes Received:
    288
    Location:
    NOTTINGHAM
    Tks xsparks. On the van consumer unit pictured the right hand RCD is off but the cables it protects are the middle ones 4cables into the block. Even with these off, when testing the RCD when switching back on the house RCD trips. Once power to van is on, when switching the right hand RCD on it trips. I think this relay energises on plugging van in initially and something happens when switching on this other circuit. Have not yet worked out what the 3rd RCD protects.
     
  14. xsparks

    xsparks Funster

    Joined:
    Mar 11, 2013
    Messages:
    132
    Likes Received:
    66
    Location:
    Gillingham
    If you're rcd on your van is working correctly it should have tripped before .It either work's or it doesn't.Imagine the rcd as a seesaw with the neutral on one side and the live on the other all is ok if the load is equal but if some of the flow travels down the earth the load becomes unbalanced and that's when it trips. 30ma trip is 30ma new or old.
     
    • Thanks Thanks x 1
  15. bertiebasset

    bertiebasset Funster

    Joined:
    Jun 16, 2014
    Messages:
    291
    Likes Received:
    288
    Location:
    NOTTINGHAM
    But the van is 10 years old so the RCD is at least 10 yrs old. The new house RCD may be very much more sensitive. will re-wire round this relay tomorrow and see it that cures it, if not will replace relay and keep looking, something is not right. :rolleyes:
     
  16. PeteH

    PeteH Funster

    Joined:
    Nov 22, 2007
    Messages:
    1,751
    Likes Received:
    2,158
    Location:
    East Yorkshire
    Normally I would agree. But My Welder Works fine on one (Split) circuit. but if I swap it to the other side? "PloP!". and it does not matter how many times I try!! Weird? or what!. So I reckon there must be some "Manufacturing" (IN?) Tolerance at work?.

    Pete
     
    • Thanks Thanks x 1
  17. peterc10

    peterc10 Funster

    Joined:
    Jul 5, 2013
    Messages:
    3,195
    Likes Received:
    2,256
    Location:
    Tunbridge Wells
    also applies to any external work like this socket.
     
    • Like Like x 1
  18. xsparks

    xsparks Funster

    Joined:
    Mar 11, 2013
    Messages:
    132
    Likes Received:
    66
    Location:
    Gillingham
    If you can try the trip on the left hand side when you push the blue button it should trip if working correctly.The other three are double pole breakers protecting individual circuits. When you locate the faulty circuit gradually break it down. In respect to the relay try to remove the out going circuit so that you can prove whether or not if it's just the relay.
     
    • Thanks Thanks x 1
  19. Lenny HB

    Lenny HB Funster

    Joined:
    Oct 18, 2007
    Messages:
    5,215
    Likes Received:
    5,010
    Location:
    West Sussex
    I
    I brought a pre-wired one didn't I guv.:)
     
  20. bertiebasset

    bertiebasset Funster

    Joined:
    Jun 16, 2014
    Messages:
    291
    Likes Received:
    288
    Location:
    NOTTINGHAM
    Will do tomorrow, will photo the relay to show 8 pins, 3 wires, all earth connected together away from relay. Only out going line I think is the one to the inverter. other is 2 ends of power input cable as far as I can see. A few loops on relay. I think it is to isolate inverter when on mains but it shunts when mains plugged in so could be an imbalance on sides (left 4 pins brown, right 4 pins blue).... tomorrow in the light.
     