HELP solar panel controller burnt out.

Discussion in 'Solar Power' started by beacons, Aug 29, 2015.

  1. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Hi today we fitted a solar panel all ok until connected to the controller
    Leisure battery then engine battery
    control panel sizzled then smoke
    all wiring correct and terminals etc
    checked why would this happen
    baird 100 w kit . Please can someone
    advise .thank you.
     
  2. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,853
    Likes Received:
    14,506
    Location:
    Leeds the one up North
    If you are 100% certain that you had made the connections in the correct order with the correct polarity then you should contact the seller
     
  3. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,853
    Likes Received:
    14,506
    Location:
    Leeds the one up North
    Have you any information to share about the controller ?
     
  4. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Hi mike took controller apart
    its a duo battery sent baird 100w kit no make visabl
    common yellow fronted with a red stripe poor quality we
    think circuit board melted.
    thanks
     
  5. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,853
    Likes Received:
    14,506
    Location:
    Leeds the one up North
    Presumably you bought from trueshopping? I found they are not unreasonable to deal with. I would expect them to offer you a suitable discount equal to the rubbish regulator. It will be interesting to see what they value it at
     
  6. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,853
    Likes Received:
    14,506
    Location:
    Leeds the one up North
  7. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    There is a 20 amp controller available would this be suitable please we will contact them monday .
     
  8. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Yes that is the one only we bought frombest eco shop
    which is part of home shopping same price I bought it over phone .thanks jan & mike.
     
  9. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,853
    Likes Received:
    14,506
    Location:
    Leeds the one up North
    100 watt panel will not exceed even 10 amps so yes but it may not be a duo controller?
     
  10. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Mike says there is a 20 amp
    controller with dual use same model but can you recommend one he said all ok
    until he conected engine battery thanks.
     
  11. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,853
    Likes Received:
    14,506
    Location:
    Leeds the one up North
    No I can't recommend a duo charger from personal experience.
     
  12. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Ok thank you for your kind help.
     
  13. jollyrodger

    jollyrodger Funster Life Member

    Joined:
    Oct 1, 2012
    Messages:
    3,441
    Likes Received:
    6,689
    Location:
    Plymouth
    A silly question ,you did connect both batteries to duo regulator first ,before connecting solar panel ? As recommended .
    I have exactly the same system 20amp duo + remote with a 200w solar battery 1(1x110amp) @20% battery 2 @ 80% ( 2 x 110 ) and no problems as yet
     
  14. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Hi thank you .no he connected solar then leisure battery all fine then engine battery
    then sizzled and smoke from controller and leads from battery is that why .?
    instructions did not state this.
    Will this of damaged panel ?we disconnected
    immediately .thanks mike.
     
  15. jollyrodger

    jollyrodger Funster Life Member

    Joined:
    Oct 1, 2012
    Messages:
    3,441
    Likes Received:
    6,689
    Location:
    Plymouth
    OK best not to mention connection sequence to seller !
    On all the regulators I've fitted it clearly states damage could occur to the unit and to connect batteries first then the panel.
    So that's the way I have always done them.all with success .
    And I always put a fuse bank in line to both the battery(s) and the panel.
    Others fit them differently .
    Can't say if the problem you have was caused by that but hope you can sort it ok (y)
     
  16. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Thank you for kind advice I will have to get a new controller there are fuses inside thecontroller are they essential ?
    Thanks.
     
  17. jollyrodger

    jollyrodger Funster Life Member

    Joined:
    Oct 1, 2012
    Messages:
    3,441
    Likes Received:
    6,689
    Location:
    Plymouth
    Fuses inside ? They didn't work then I recon from what you describe ,would have just blown and no juice would it not?
    I have fitted a 6 fuse unit in line ,pull all fuses connect all wiring put in batt fuse's first then solar panel .
     
  18. Wildman

    Wildman Read Only Funster

    Joined:
    May 30, 2008
    Messages:
    15,458
    Likes Received:
    8,598
    Location:
    Ilfracombe, Devon
    only if you connect the solar first, hee hee
     
  19. beacons

    beacons Funster

    Joined:
    Jan 27, 2014
    Messages:
    806
    Likes Received:
    640
    Location:
    mid wales
    Thank you will get inline fuses hopefully
    will get sorted out thank you for your kind advice.
     
  20. SomeoneElse

    SomeoneElse Funster

    Joined:
    Apr 22, 2013
    Messages:
    572
    Likes Received:
    375
    Location:
    Cotswolds
    Hi,
    The manufacturers instructions are not the best and are therefore not very clear. What pages two and three of the manual is trying to say is to connect the terminals in order 1 through to 6. IE terminal 1 first, followed by terminal 2 etc. The reason the battery(s) must be connected first is to enable the elctronics to automatically select 12 or 24V mode.
    Manual is here http://www.epsolarpv.com/en/uploads/news/201310/1382338230686012.pdf

    The specification of the unit is here http://www.epsolarpv.com/en/uploads/news/201408/1407810914399200.pdf
    Claims "the failure rate is less than 2 per 1000 pcs" and also claims " Electronic protection: over charging, short circuit, battery reverse polarity protection".
    Nothing about panel reverse connection!
     