gas (1 Viewer)
blucamp2
42
happy New year Funters .
Just getting M/home ready to leave on monday for spain ...
having trouble getting the Gas to work properly I have the scu- motion ( truma reg) I can get the gas to work but if I put heating and cooker on then it stops and I have to prime the system again ... could it be the weather as its minus 5c I am using propane
it works ok on just cooker or just heating
regards
phil
43,301
49,287
cant see it being the propane as that will still vapourize at a lower temperature than you could stand for any length of time.
maybe a faulty regulator.
is the regulator lower than the bottle valve ?
if so it could be the reg is partly clogged with the rubbery crap that comes from the hose causing a restricted flow.
scotjimland
2,255
9,771
A Woosh bang
the lower the ambient temperature the lower the evaporation rate of the propane, with both heating and cooking you have exceeded the take off rate, not a lot you can do about it unless you can fit a bigger bottle which would give a higher take off rate.
jim
DESCO
2,646
266
London
low profile
18 years +12 years tugging
jim
Agree with Jim on this one, I have the Truma system have found the same, as gas cupboard is in heated garage once the cupboard gets warm through panels problem vanishes and then works OK.
Dave :thumb::thumb:
43,301
49,287
jim
sorry Jim, got to disagree.....
at -18deg C propane vapour will still be at a pressure of 24psi in the bottle.....
at -42 C there will be next to no pressure.
we only need 30millibar......1/66th of the bottle pressure.
even an 'open to air' bottle valve will release more gas than we need in a given time.
read the chart...table one.
scotjimland
2,255
9,771
A Woosh bang
then we will disagree John
the max take off rate is directly proportional to the bottle size AND the temperature.
bottles deliver gas at different rates - it's impossible to run all appliances simultaneously from the smaller bottles but is no problem with the larger ones. These rates will fall as the temperature drops below 20c
Propane Take off rates at 20c.
3.9 Kg = 0.28 m3/h (7.5 kW)
6.0 Kg = 0.42 m3/h (11 kW)
13 Kg = 0.57 m3/h (15kW)
blucamp2
blucamp2
42
Thanks guys ,I have a Danish system which is the same as the spanish.
I had a gas test done in november as part of the hab serivce .have had no problems with it before So I am inclined to agree with Desco and Jim , I think i was a little on the high side when I said minus 5c its more like minus 8/10c I had to put a heater in the Gas locker to get it to work So we will just have to cook or kept warm until we get out of this frost .. I can always if the problem continues once we get south I can get it sorted on the way .. Thank you papajohn for your posts and had I not had this truma system I would have gone with your theory
thanks guys
phil