a coiled cable, ie...on a drum or tightly wound etc, is dangerous but a loosely coiled cable should be ok.
make each loop around 1 mtr and spread loosely on the ground ...still quite tidy and out of the way.
tightly coiled inner loops on a drum get no cooling air and will overheat.
This subject has been covered in depth on another forum, I thought that I would paste a couple of their posts, Have a read it could be useful.
QUOTE::welcome:
There is no appreciable external magnetic field generated by a coiled three core cable. The fields generated by the neutral current core mostly cancelling the field generated by the live current core which is why a clamp meter only works on single cores. The heating effect is solely due to bunching of the cables as I have explained earlier in the thread.
As the current flowing in one direction through the live wire is exactly the same as the current flowing in opposite direction through neutral (otherwise the RCD would trip), the magnetic fields from live and neutral cancel out each other.
The only thing that determines the "heating power" of the whole cable is the "ohmic" resistance of the wires, multiplied with the current to the power of 2. So if you go from 4 amps to 16, the current increases by a factor 4 and the heating power by a factor 16!
For the total amount of heat generated it does not matter whether the cable is coiled up or not.
I agree the amount of heat generated is the same what matters is the amount of heat escaping as I'm sure you agree.
[FONT="]The key perhaps to understanding it is to think about the fact that the same current is flowing in all the cable so the same amount of heat is being produced throughout its length.
When coiled
Only the turns of the cable at the top have an air surface to give off their heat to.
Turns of the cables at the bottom and sides may have part of their surface touching a heat conductor and will fare better.
Turns in the middle are surrounded by other turns all heating up. So as heat can only flow from hot to cool there is nowhere for the heat to go and the temperature rises.
In the attached sketch shows a cross section of the coill with the middle turns heating up[/FONT]
Its a while since I have had a copy of the Regs to hand but when I inserted the amendment that brought in caravan sites I believe there was reference to the colour of the outer sheath (which may or may not have been subsequently amended).
Anyway just from the photo and the evidence I have produced it looks like more than 25m on the reel para 11 and there is no notice para 3.
Note also that this part of the regulations Special Installations is preceded by an introduction and I think this is a accurate precis
The Regulations apply to all electrical installations in buildings. There are some situations out-of-doors, as well as special indoor ones, which are the subject of special requirements due to the extra dangers they pose, and these will be considered in this chapter. These Regulations are additional to all of the other requirements, and not alternatives to them.
However my remark that you quoted was merely throwaway, PeeJay's installation looks good to me, but perhaps intended to deter DIY reel makers to meddle in stuff they don't understand.
[FONT="]When a cable is rated consideration is given to:
How hot the copper core will get at a range of ambient temperatures, at a range of currents.
The heat transmission properties of the insulation
The melting properties of the insulation.
How the various wires perform when made into a (say 3 core) cable.
A max rating is arrived at for the cable in free air at say 20 degrees C. At that max rating enough heat will be given off by the outside of the cable to keep the temperature inside within specification (max about 70 degrees C for PVC/PVC insulation) Anything that stops this heat escaping will at the max rating rapidly lead to the cable melting.
They then produce a specification.
It follows from this that the effect of warm cables even fairly loosely wound on a reel will affect all the turns of the cable preventing the heat from escaping and therefore the insulation gets very quickly to its melting point.
A short between the two hot wires of a three core cable (Live and Neutral) won't trip the RCD but will trip the main MCB. If there is enough energy at the point of the short circuit a fire may start before the removal of current allows the whole thing to cool.
Derating the cable when wound on a cable to around 50-55% of it max rating is done because 8A run through a 16A cable wound up won't get any hotter than 16A when laid out.
edit added "at a range of currents'[/FONT]