    Not MH orientated but electronics so I am putting this question here in case any wiring experts can help.

    I am tidying up the wiring to a TV by putting the cables behind the plasterboard. There will be one 3 gang little socket carrying the coax signal, an HDMI socket and an Ethernet socket. There will then be another socket for the 13A mains.

    I only have to run the cables a maximum of about 2m horizontally to where the router and blu-ray player will sit and it will save me quite a bit of plastering if I can hide them all in a single run. The plan is to cut slots over the vertical wooden battens behind the plasterboard and "fish" the cable to the next batten. This should only leave me with about 3 short slots to plaster over afterwards.

    My question is will having the mains and the Ethernet cable, which is Cat 6 be a problem over such a relatively short distance if they are close together?

    I have read you should keep them at least 300mm apart and if they have to cross they should do at right angles. The Cat 6 cable is unshielded.

    I suspect I am just being lazyand need to cut separate channels for the mains but if anyone has any experience of this I would be grateful for advice.
     
  2. canopus

    canopus Funster Life Member

    Joined:
    Nov 27, 2010
    Messages:
    2,825
    Likes Received:
    3,200
    Location:
    Lincolnshire
    Golden rule don't run mains and comms cables in close proximity. :thumb:
     
    • Like Like x 2
  3. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,857
    Likes Received:
    14,508
    Location:
    Leeds the one up North
    It will be fine
    I've run mains and data all over on seperate trays and then when it gets to the desks or dado trunking it's all in plastic two or three compartement trunking with no metal fillet. I've never know a data man complain yet.
     
    • Like Like x 1
  4. scotjimland

    scotjimland Funster Life Member

    Joined:
    Jul 25, 2007
    Messages:
    28,934
    Likes Received:
    25,574
    Location:
    .
    The golden rule is to run mains and coms. in separate ducts, .. however,

    I've done a similar run to my TV using about 6ft of mini trunking. Mains, LAN , HDMI, TV aerial, and a USB cable and had no problems..
     
    Last edited: Feb 21, 2014
    • Like Like x 1
  5. sdc77

    sdc77 Funster

    Joined:
    Jan 28, 2013
    Messages:
    2,486
    Likes Received:
    2,893
    Location:
    East london
    Can't imagine you'll have any probs over that distance. Main probs are good termination of your cat 6 cable and avoiding sharp bends.
     
    • Like Like x 1
  6. TheBig1

    TheBig1 Funster Life Member

    Joined:
    Nov 27, 2011
    Messages:
    7,222
    Likes Received:
    9,602
    Location:
    Dorset
    you will only pick up data noise if the mains cabling is badly connected or damaged. in reality any network card is capable of being affected by mains hum but they filter it out. what you want to really avoid is running a data cable close to a transformer

    what you are suggesting should be fine... been doing similar for years without issues
     
    • Like Like x 1
  7. John Laidler

    John Laidler Funster

    Joined:
    Jan 9, 2013
    Messages:
    8,574
    Likes Received:
    11,553
    Location:
    Plympton, Devon
    Many thanks for the input. Just put the 13A cable in and it was a lot easier than I expected. So if the men's curling team can only manage silver (as it looks but fingers crossed) I'm going for gold and will separate them. This should give me more holes to fill but hopefully they will be smaller holes!

    Will post picture of my butchery later for your amusement.
     
    • Like Like x 1
  8. Ed Excel

    Ed Excel Funster

    Joined:
    Nov 27, 2012
    Messages:
    869
    Likes Received:
    577
    Location:
    Ribble Valley
    The issue of separation of structured wiring cabling and low voltage cables is more about safety than performance. You need to keep them a reasonable distance apart to avoid accidents happening in the future to some unsuspecting DIYer/tradesman. 230V on your CAT6 cable would be dangerous. Separation will have a double benefit in that interference on your data cabling should, also, not be a problem, although, CAT6 cable is layed up (twisted) to avoid the conductors running parallel with others.

    PS glad to see you are going to separate them.
     
    Last edited: Feb 21, 2014
    • Like Like x 1
  9. cmcardle75

    cmcardle75 Read Only Funster

    Joined:
    Jun 8, 2012
    Messages:
    670
    Likes Received:
    263
    Location:
    Reading
    It will work fine electrically. The frequency is so low on the mains cable that it will not interfere with the UHF signals on the network cable.

    However, it is not permitted for safety reasons. You must have two insulation resistant sheaves between the conductors. The mains cable will have one, but your Cat 6 will not count, as the outer layer is too thin. You could run the mains cable (or the network cable) in conduit to solve the problem.
     
    • Like Like x 1
  10. John Laidler

    John Laidler Funster

    Joined:
    Jan 9, 2013
    Messages:
    8,574
    Likes Received:
    11,553
    Location:
    Plympton, Devon
    Again, many thanks, I hadn't really considered the safety aspect but having once but a masonry drill through a 30A cooker feed (spectacular!) I can see the point. I remember years ago when I was serving in Belize the lights of our mess bar were forever flickering but no one really bothered as a thump on the bar usually worked. That the building was made of wood with a thatched roof never entered the discussions. A few days before I left they did some renovation and prising off a plywood panel in the bar they found the mummified remains of a rat - with its teeth wrapped around the mains cable. It would be nice to think it is still there in a glass case behind the bar but I suspect it was binned.

    Today, with one ear tuned into the curling (hard to argue with the result) I have finished most of the preparatory work. The picture below shows what it looks like at the TV end, which is hidden behind the dog blanket. There are 3 slots in total for each cable over the vertical battens behind the plaster board. The smaller square opening will hold the low voltage stuff and the lower one will be for a twin 13A socket. They are about a foot apart. I haven't added a second layer of insulation as recommended and will plead ignorance if the house burns down. I think the risk is low as the current(!) family plans are we will stay here until carried out feet first so what subsequent owners get up to is their problem.

    The top run has the co-ax in and the bottom run has the 13A ring main threaded. I need to add the Cat6 Ethernet cable and the HDMI cable to the top run. The HDMI is going to be fun. I have ordered some HDMI sockets but you don't seem to be able to buy bare HDMI cable so I will cut the ends off an existing cable and hopefully can connect that to the sockets. HDMI seems to be a bit of a mish-mash, four twisted pairs and seven additional separate conductors, fifteen wires in total. If all else fails I will just pull a standard HDMI cable with plugs on the ends through and have the ends waving around as tails, so to speak.

    Anyway, the main point of this long-winded post is to extol the virtues of a magical tool which I had heard about but have never used.

    You will see in the picture below the lower holes have ragged edges. These were done by hand with a pad saw. This worked fine but I was then lent an oscillating saw - one of these http://www.feinus.com/en_us/oscillating/multimaster/fein-multimaster-top-0297187/

    It quickly produced fine cuts in the plaster with very neat edges. I also used it to cut into the battens so I can chisel them out tomorrow to give more space for the three cables. It doesn't produce much dust, a fraction of what an angle grinder would make, although it does get into the air a bit so covering things up is advised.

    If I ever need to cut holes in plaster board again I might buy one, ScrewFix sell cheapies which are good enough for light use I am told but the blades, whatever saw you have, are not cheap. Hit a screw at your peril - I was lucky today and can hand it back undamaged. The lower picture is of the tool itself - note some dust but not too much.

    Apologies for the large images.


    [​IMG]


    [​IMG]
     
    Last edited: Feb 21, 2014
    • Like Like x 1
  11. Ed Excel

    Ed Excel Funster

    Joined:
    Nov 27, 2012
    Messages:
    869
    Likes Received:
    577
    Location:
    Ribble Valley
    Neat job. I see you only have one power cable which I assume you are spurring off an existing socket on a ring-main circuit. I don't imagine you will want to use the dual socket you are installing to its full capacity, but wiring in this manner limits the load to 13A; Connect more and you will overload your cable. Again, you now know this, but others won't. If you have spurred off the ring with a 13A connection unit, forget the above.

    Like the oscillating saw!
     
    Last edited: Feb 21, 2014
  12. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,857
    Likes Received:
    14,508
    Location:
    Leeds the one up North
    Does not need a fused spur. On site guide appendix 8.2.4 allows a twin socked outlet unfused.

    BTW 2.5 T&E is rated at 27amps and for a short spur it will easily carry the ring circuit mcb rating of 30/32amps
     
    Last edited: Feb 21, 2014
  13. Ed Excel

    Ed Excel Funster

    Joined:
    Nov 27, 2012
    Messages:
    869
    Likes Received:
    577
    Location:
    Ribble Valley
    Surely your figures demonstrate it will not carry the load you suggest. Also, it will carry less when derating factors are applied.
     
  14. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,857
    Likes Received:
    14,508
    Location:
    Leeds the one up North
    No they don't if you read it carefully. As I said it is permitted by BS 7671
    Also the most you can draw from a twin socket is 26 amps
     
    Last edited: Feb 21, 2014
  15. Ed Excel

    Ed Excel Funster

    Joined:
    Nov 27, 2012
    Messages:
    869
    Likes Received:
    577
    Location:
    Ribble Valley
    Still not sure 2.5, derated, would be sufficient. I would use 4.0sq mm in this instance. BS7671 is a basis for engineering designs not an installation manual.
     
  16. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,857
    Likes Received:
    14,508
    Location:
    Leeds the one up North
    Derated for what? I've never in 40 years met a derated ring main :Rofl1:
     
  17. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,857
    Likes Received:
    14,508
    Location:
    Leeds the one up North
    Of course if in doubt? ask an electrician :thumb:
     
  18. geo glasgow

    geo glasgow Read Only Funster

    Joined:
    Feb 2, 2014
    Messages:
    292
    Likes Received:
    273
    Location:
    Glasgow
    before running in wall conmnect everything up

    the way it would be when completed switch all of your products and sources on
    switc your hdmi switch or sources over and use the various hdmi on tv screen
    does the system put out video or audio interference ,
    yes? the screen power and video separate iv never needed to but separate first to see if it then works perfect ,
    NO? WORKS perfect then your good to go,, remember you can screen all cables if required, foil. or cable management trunking again over this lenth im sure all work work great,, . good luck any issues let me know i can assist you
    but would need to know all sources your using,,:thumb:
     
  19. daveandsan

    daveandsan Funster

    Joined:
    Dec 10, 2013
    Messages:
    1,237
    Likes Received:
    1,772
    Location:
    South Staffs
    Excuse my ignorance but i didn't think anyone but a qualified electrician was allowed to put spurs in now under the new regulations. I wouldnt think your insurance would be very happy if something untoward was to happen.
    :Smile:
     
  20. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,857
    Likes Received:
    14,508
    Location:
    Leeds the one up North
    A spur is permitted by a competent person, it does not have to be an electrician. A test certificate would be useful :thumb:
     