CAN YOU USE PTFE TAPE ON GAS CYLINDER CONNECTION?

Discussion in 'Motorhome Chat' started by wingman, Jul 2, 2014.

  1. wingman

    wingman Funster

    Joined:
    Feb 10, 2013
    Messages:
    971
    Likes Received:
    2,363
    Location:
    Romford, Essex
    Can one use PTFE tape to ensure a gas-tight fit on the cylinder union? The brass hose-to-cylinder connection never seems competent enough to me. Yes, I take care of my brass hose coupling, but the cylinders must get plenty of abuse from previous owners? Even the slightest dinge (technical term?) on the cylinder coupling could allow gas to escape.

    Certainly, there have been a few times that I've had a whiffy gas locker - even though it's vents are clear and hose etc is new. A dealership once told me that "you have to really nip the nut up tight with a spanner". Well, I've given my spanner and nut plenty of 'Isaacs' and even hung off it a-la Robin Knox Johnston! BUT a brass- to-brass connection seems doomed to fail at some stage, especially with road movement and metal-metal imperfections.

    I'm aware that there's two different types of PTFE - one for general plumbing and one for gas. Sooo, apart from getting over-zealous with tape and blocking up the aperture, is there any reason why tape can't be used
     
  2. scotjimland

    scotjimland Funster Life Member

    Joined:
    Jul 25, 2007
    Messages:
    28,934
    Likes Received:
    25,574
    Location:
    .
    No.. do not use PTFE on a bottle seal..

    the seal on a propane bottle is a brass, face to face seal.. the thread does not make the seal..
    As the bottle seal is female connection.. it is unlikely and unusual for it to be damaged..
    the seal on your pitail or regulator, which is male, is far more likely to get damaged..

    Inspect the male, if it is scored either replace or if only minor scratches, try rubbing with some very fine emery cloth..
     
    Last edited: Jul 2, 2014
    • Like Like x 1
  3. tofo

    tofo Funster

    Joined:
    Oct 1, 2007
    Messages:
    6,599
    Likes Received:
    6,226
    Location:
    Kirby cross further from londin
    I always assumed you shouldn't

    As the faces of the joint

    Are ground to fit each other

    tape on the thread won't stop gas coming from
    The inner gas carrier pipe on the connection

    Only my thoughts
     
  4. Terry

    Terry Funster

    Joined:
    Dec 27, 2007
    Messages:
    10,722
    Likes Received:
    6,224
    Location:
    South yorks
    Well I disagree with Jim on this :D cannot see what harm it can do and yes use the gas stuff --I would buy yourself a can of gas leak detector spray as well --I know I have given some of my own bottles plenty of torques but still detected the odd wiff of gas in the locker ---The gas SS pipe I just got off Tecno has a rubber connection on the bottle side and hand tighten knob/no spanners so I cannot see why no PTFE
    I can stand to be corrected it won't be the first time :Dedit I am assuming you mean on the threaded bits
    terry
     
  5. Gromett

    Gromett Funster

    Joined:
    Feb 27, 2011
    Messages:
    7,941
    Likes Received:
    14,016
    Location:
    UK
    I was always led to believe no PTFE on any gas connection. Plumbed in my whole van 3-4 years ago and no problems at all.
    Occasionally got a smelly bottle before I started on the refillable, but a quick tweak always sorted it.
     
    • Like Like x 1
  6. scotjimland

    scotjimland Funster Life Member

    Joined:
    Jul 25, 2007
    Messages:
    28,934
    Likes Received:
    25,574
    Location:
    .
    no problem.. as is your prerogative .. :)

    I don't give advice on topics I have no qualifications, training or experience.
     
    • Like Like x 1
  7. The Wino

    The Wino Funster

    Joined:
    Mar 23, 2012
    Messages:
    1,117
    Likes Received:
    2,004
    Location:
    leicester

    The seal is the face of the domed end so ptfe wont help it might mean you cant tighten the connector fully so no (in my opinion).

    David
     
    • Like Like x 1
  8. scotjimland

    scotjimland Funster Life Member

    Joined:
    Jul 25, 2007
    Messages:
    28,934
    Likes Received:
    25,574
    Location:
    .
    you have it in one.. (y)

    There is another valid reason for not using PTFE tape,
    If a small part of it gets into the pipework it can block the regulator or a gas jet causing all sorts of problems..

    PTFE should only be used on taper threads where it is used as a lubricant and sealer.. taking great care not to wrap it over the edge of the thread where it could break off when tightened. .. (see above).

    Never use on parallel threads or gas compression joints .
     
    Last edited: Jul 2, 2014
    • Like Like x 1
  9. Jaws

    Jaws Funster Life Member

    Joined:
    Sep 26, 2008
    Messages:
    18,347
    Likes Received:
    21,717
    Location:
    Narrfoook
    No. one son is a gas safe approved fitter.
    I asked him about this a while ago.
    There is a specific type of ptfe tape made for gas joints and ordinary white stuff should not be used ( an installation will fail commissioning tests if it is used and they will not issue a Gas Safe certificate )

    But as others have already mentioned, the seal is on the domed end not the thread
     
  10. Terry

    Terry Funster

    Joined:
    Dec 27, 2007
    Messages:
    10,722
    Likes Received:
    6,224
    Location:
    South yorks
    The gas PTFE IS BLUE -still don't see any reason it cannot be used on the threaded bits -we always use gas it paste on any of the compression /olives joints but that stuff is red and gets everywhere -I have several mates who are gas safe reg and I admit I did not know they even did a gas PTFE tape until a couple of yrs ago -so will ask them about it's use
    terry
     
  11. Plumberman

    Plumberman Read Only Funster

    Joined:
    Sep 29, 2013
    Messages:
    66
    Likes Received:
    40
    Location:
    West Midlands.
    Hi Wingman,
    PTFE tape should not be used on Gas Unions as there is a risk if it stopping the two machined faces of the union sealing properly.
    Also as posted earlier there is a risk of causing a blockage in the connecting pipe work / fittings.
    You can use an approved LPG jointing paste if you have problems with leaks but be careful not to get any inside the pipe work ,just a very light coating should do the job.
    PTFE is only a thread sealing tape.
    If you smell gas in your Gas locker buy a can of leak detection spray which is quite cheap from a plumbers merchants and will detect where the leak is coming from.
    Leaks will show up by foaming bubbles around the leaking areas,even micro leaks can be dangerous if allowed to build up.
    Don't be tempted to use washing up liquid as an alternative as this has been proved to be corrosive to hoses and fittings .
    This should be used every time you undo or disturb a fitting.
    LPG is heavier than air so gas will collect at the lowest point,which is why you should have drop holes under all cylinders and appliances which should be kept clear of debris at all times.
    Also the base of cylinders should be kept clear as this is an integral part of the surface area of the cylinder to allow gas to be drawn off at the correct rate.
    The sealant mentioned by Terry in previous post is Stag Red Sealant and is for use on permanent joints not cylinder unions .
    Most modern sealants are non setting to allow for easy removal of fittings.
    Hope this helps you.
    Alex.
     
    Last edited: Jul 2, 2014
    • Like Like x 3
  12. Tootles

    Tootles Funster

    Joined:
    Sep 14, 2013
    Messages:
    9,003
    Likes Received:
    30,944
    Location:
    Lancaster

    Tyres????? :whistle::whistle::whistle:
     
  13. wingman

    wingman Funster

    Joined:
    Feb 10, 2013
    Messages:
    971
    Likes Received:
    2,363
    Location:
    Romford, Essex
    Thanks Alex and all other contributors. Really interesting replies.
    When I'd sat down and thought about it, all made complete sense, doh!

    What was equally interesting (and quite a gem) was the locker space itself. I've always understood about keeping the vents clear and I have two contoured platforms for the cylinders BUT, I have a bad habit of using the locker to bung all sorts of stuff. As of now, I've stuffed in levellers, a flat hose reel, dust sheet to kneel on and an adjustable parrot-nosed spanner contained in anti-rattle bubble wrap to give the nut a few more Newtons!!! The locker's not full, but the advice about an air flow around the bottles is something I've never thought about!

    Bugger; where am I going to put this stuff now???

    Thanks guys
    James
     
    • Like Like x 1
  14. Terry

    Terry Funster

    Joined:
    Dec 27, 2007
    Messages:
    10,722
    Likes Received:
    6,224
    Location:
    South yorks
    Spoken to 3 different gas safe plumbers now and all say it's safe to use on the threaded bit ---It is now white tape but comes with a yellow top and is slightly thicker than normal PTFE, normal ptfe which incidentally is pressure tested up to 20 bar where gas is normally at 2 bar at the most -All 3 said gas is measured in millibars unlike water and all said it was OK to use or use the paste just be careful not to get the paste into the pipe :)All said use the leak detector spray after making the seal if you are unsure,
    terry
     
  15. funflair

    funflair Funster Life Member

    Joined:
    Dec 11, 2013
    Messages:
    4,488
    Likes Received:
    4,745
    Location:
    Guisborough
    I think the question has to be WHY would you want to put ptfe tape on the thread as it will not help with a gas seal, if the male into female joint is leaking the threads are not there to stop it as gas would still get up the inside of the nut.

    To lubricate the threads OK.

    Martin
     
  16. mentaliss

    mentaliss

    Joined:
    Nov 2, 2012
    Messages:
    657
    Likes Received:
    307
    Location:
    Lancing
    Well can't speak for the others BUT GasLow ( my system) technical says absolutely not !!!! no tape, no sealing gue..........
     
  17. gasman2008

    gasman2008 Read Only Funster

    Joined:
    Aug 5, 2012
    Messages:
    126
    Likes Received:
    98
    Location:
    Southampton
    If you suspect a leak cover the joint with leak detection fluid, if you want to help the seal put a small (VERY) amount of gas tap grease (this must be for 3rd family gas) on the male end before you put the hose onto the bottle
     
  18. Techno

    Techno Funster Life Member

    Joined:
    Jul 28, 2010
    Messages:
    13,859
    Likes Received:
    14,514
    Location:
    Leeds the one up North
    Shall we have a vote?
    No tape !
     
  19. gasman2008

    gasman2008 Read Only Funster

    Joined:
    Aug 5, 2012
    Messages:
    126
    Likes Received:
    98
    Location:
    Southampton
    Tape will not help. So I vote NO
     
    • Like Like x 1
  20. timdownieuk

    timdownieuk Funster

    Joined:
    Apr 9, 2013
    Messages:
    612
    Likes Received:
    326
    Location:
    Ayr
    Given that these gas safe plumbers have no idea about cylinder pressures I wouldn't put too much store in anything they say. Were they qualified to work with LPG? Not all are I believe.

    I vote NO too. As has been repeatedly said, the threads don't make the seal.
     