I have panels on my house but would like advice on using them on the van? How do they connect to the electrical supply of the van, are they a DIY or dealer fit? Any advice would be gratefully accepted :)
Hope everyone's enjoying their festivities!
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Your domestic panels are a higher voltage than those suitable for your van, they are connected to a grid tied inverter that converts your solar array into a voltage suitable to feed back into the mains system

For your van you need panels that can be used with a 12 volt regulator that will then charge your leisure batteries. They will not feed your mains sockets.
 
OP
OP
SteveG

SteveG

Free Member
Dec 22, 2014
79
54
NW England
Funster No
34,542
MH
Coachbuilt
Exp
Newbie
I know 12v panels are needed not the ones on my house! ;-) are they a DIY job do you think?

Subscribers  do not see these advertisements

 
Feb 8, 2014
1,661
4,630
Sheffield
Funster No
30,022
MH
Eldis Majestic 115
Exp
Vans and tugs since mid 70's
fitted an additional panel to mine so that the panel lifts on and off. wired to controller then to leisure batteries. The directions were in good English and very clear. If I'd realised sooner on this recently acquired van I could have possibly wired it directly to the MH EC500 PSU same as the permanently fixed one. Its only a 42w panel but when angled southwards I reckon it matches the output from the 100w fixed panel.
 

Jaws

LIFE MEMBER
Sep 26, 2008
23,821
71,968
Thetford Norfolk
Funster No
4,189
MH
C class, Chieftain
Exp
since 2006 ( I think ! )
Only real strong advice I would offer is to get the very best controller you can buy
Skimping on the controller is false economy as a lot of the power generated by the panels will end up being wasted

Subscribers  do not see these advertisements

 

Munchie

LIFE MEMBER
Jul 28, 2007
8,921
12,581
Camping Les Vigeres
Funster No
26
MH
Font Vendôme
Exp
Since 2004
My controller is a sunsaver 20.

My intention is to wire em in series! I.E. pos to neg on next panel and so on so should not have to join wires or make any holes.
 
Apr 22, 2013
911
660
Cotswolds
Funster No
25,654
MH
Bailey Approach 625
Exp
Since 2011
My controller is a sunsaver 20.

My intention is to wire em in series! I.E. pos to neg on next panel and so on so should not have to join wires or make any holes.
RTFM
If its a Morning Star corporation SunSaver controller then its uses PWM technology and can only take a input of 25 Volts, so you must connect the panels in parallel.
To enable you to connect panels in series you need the more efficient MPPT techology.
 
Aug 30, 2012
4,270
11,303
Home of the war horse
Funster No
22,676
MH
burstnar T640
Exp
2010
My controller is a sunsaver 20.

My intention is to wire em in series! I.E. pos to neg on next panel and so on so should not have to join wires or make any holes.
I dont "think" you can do that
In series will step voltage up
So if you linked all 3 in series you would have 36 volt
Would that not decrees Amps to about 8 or would controller take care of that
I was not told not to do it but I may be wrong elecctricery is not my thing
It may be my controller that can't handle it

Subscribers  do not see these advertisements

 
Sep 23, 2013
2,579
8,603
Lincs
Funster No
28,231
MH
Globecar Campscout
Exp
Since 2008 (started in a VW T4 campervan)
It can be done & can usefully extend the time of year panels produce something meaningful, especially if you will be anywhere in Northern Europe.

But - you must have a MPPT controller & it must be capable of handling the SUM of the voltages produced by each panel. That leaves you with a fairly short short-list of fairly expensive controllers, but it's the way to go if you want to wild camp out of season. It can't work miracles though.

Something like this.
 

Munchie

LIFE MEMBER
Jul 28, 2007
8,921
12,581
Camping Les Vigeres
Funster No
26
MH
Font Vendôme
Exp
Since 2004
Have decided to wire in parallel and our 20 amp controller will be ok at this time of year.
Will just link the pos together from panel to panel then the negs and to the controller
Will buy a 30 amp mppt when we get home.

Thanks
 
Last edited:
Mar 26, 2009
8,130
11,168
Yr Wyddgrug
Funster No
6,057
MH
Hymer B678DL
Exp
Since 2009
Something like Broken Link Removed can be used to connect up to an existing installation.

Subscribers  do not see these advertisements

 

Wildman

Free Member
May 30, 2008
0
8,470
Ilfracombe, Devon
Funster No
2,913
MH
Amazon Ambassador
Exp
since 1967
Something like Broken Link Removed can be used to connect up to an existing installation.
excellent
fitted an additional panel to mine so that the panel lifts on and off. wired to controller then to leisure batteries. The directions were in good English and very clear. If I'd realised sooner on this recently acquired van I could have possibly wired it directly to the MH EC500 PSU same as the permanently fixed one. Its only a 42w panel but when angled southwards I reckon it matches the output from the 100w fixed panel.
Connection should be to the battery first and solar panel last

My controller is a sunsaver 20.

My intention is to wire em in series! I.E. pos to neg on next panel and so on so should not have to join wires or make any holes.
an autosensing 12/24v controller would handle them connected in series.
 
Apr 22, 2013
911
660
Cotswolds
Funster No
25,654
MH
Bailey Approach 625
Exp
Since 2011
an autosensing 12/24v controller would handle them connected in series.
Err NO!
The autosensing bit is on the battery side, so with a 12V battery you need a maximum of 36 cells in series, panels with 36 cells are usually refer to as 12V panels.
A MPPT controller handle higher voltage panels or panels in series. The controller manual will specify the maximum wattage of the panels that can be connected.
 

Wildman

Free Member
May 30, 2008
0
8,470
Ilfracombe, Devon
Funster No
2,913
MH
Amazon Ambassador
Exp
since 1967
Oops, thats what goes of replying with a thick head in the morning unless of course your batteries are connected in series but the outputs are taken across one battery only.

Subscribers  do not see these advertisements

 

Munchie

LIFE MEMBER
Jul 28, 2007
8,921
12,581
Camping Les Vigeres
Funster No
26
MH
Font Vendôme
Exp
Since 2004
The instructions for my regulator says batteries last! i am now lost!

Subscribers  do not see these advertisements

 

Munchie

LIFE MEMBER
Jul 28, 2007
8,921
12,581
Camping Les Vigeres
Funster No
26
MH
Font Vendôme
Exp
Since 2004
Just reread the instructions.
Two pages on it says first!!! Must be a misprint on the earlier page!!!
So will go with first!!!
 

Peter A Forbes

Free Member
Nov 23, 2014
270
184
Rushden, Northants, UK
Funster No
34,314
MH
Mercedes 614D
Exp
10+
The MPPT controllers that we have, and Andy (techno100) have an operating input voltage range up to about 33V and a 'Do Not Exceed' voltage of 55volts.

We tried series connecting panels a couple of years ago, when we were fitting the trailer out. It didn't work.

The current build has 4 X 100W panels feeding two MPPT controllers. We originally planned for a 220AH leisure battery but two more 6V 220's came along for free so we will have 440AH worth of batteries in total.

Panels picture:

Broken Link Removed

Previous build on the trailer (which we still have)

Broken Link Removed

Andy was the source of much help and information when we did the trailer, for which we are very grateful.

Peter

Subscribers  do not see these advertisements

 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
For what it is worth I have never tried the series option despite that mppt being marketed as capable. I have plenty of panels laid up so I might connect a set up next month on my decking and see what develops .The reason I didn't go for series was the problem of having 3x100 watt panels which in series would be far too high a voltage.

This is the regulator Broken Link Removed

As you will see it can handle a maximum OPEN circuit voltage of 50
12 volt panels have open circuit voltages of under 22volts so 2 in series should work in theory
 
Last edited:

Peter A Forbes

Free Member
Nov 23, 2014
270
184
Rushden, Northants, UK
Funster No
34,314
MH
Mercedes 614D
Exp
10+
@Peter A Forbes - what was the problem with the series connection?

Which controller did you have? The same 33V ones?

Yes, the same as Andy has.

Max MPPT input is 33V, Absolute Max withstand input 55V.

The normal panel would output 18V or so, with two in series you'd straight away exceed the MPPT voltage for the controller and it shuts down.

Peter

Subscribers  do not see these advertisements

 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
Where does it say 33volts in the manual Peter?
It quotes max open circuit voltage 50 which is fine for series
 

Techno

LIFE MEMBER
Deceased RIP
Jul 28, 2010
15,475
20,752
Leeds the one up North
Funster No
12,905
MH
Rapido 7090F 3 litre 160
Exp
May 2010
I see now you have the MKII model
The later one and current model is 15 to 37 volts mppt.

EDIT I see from your picture in the other thread that you have a MKII on the left & a MKIII on the right. The later model also has an always on display and a backlight when needed.
 
Last edited:
Sep 23, 2013
2,579
8,603
Lincs
Funster No
28,231
MH
Globecar Campscout
Exp
Since 2008 (started in a VW T4 campervan)
I have plenty of panels laid up so I might connect a set up next month on my decking and see what develops
It would be a good time to run some trials while there isn't a lot of sun about.

Comparing the output from the same two panels wired first in parallel then in series while the sun is low intensity should show if it's worth doing - or more precisely, whether it's worth paying the extra for a regulator that will take the higher input voltage.

As the sun increases in strength, there should be a period when the series wired pair begin providing sufficient output voltage to start the charging process while a parallel wired pair wouldn't produce enough to start charging.

Once there is sufficient sun for the parallel wired pair to start charging as well, I'm guessing that there is little difference between the two methods, but I don't really know.